Results 1 to 6 of 6
Thread: Ceiling Fans and Sprinkler Heads
  1. #1
    Join Date
    Nov 2010
    Allentown, PA
    Posts
    79
    Commercial application.
    What is the minimum clearance that a ceiling fan may be installed from a sprinkler head?
    3ft from SD.
    Ceiling height ≈ 9ft
  2. #2
    Join Date
    Nov 2009
    Moore, OK
    Posts
    432
    NFPA requires 18" clearance, both underneath and horizontally, but they are talking about "materials" being stored. I wouldn't think a ceiling fan would be an issue unless it's directly underneath the fan which would obstruct the sprinkler spray pattern.
    I have no idea what building codes say though.
    -Mark
    Industrial Occ. Safety & Health
    "Remember to pillage before you burn"
  3. #3
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,191
    Look at NFPA 13, Section 8.6.5.2.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #4
    Join Date
    Nov 2010
    Allentown, PA
    Posts
    79
    Thank you for the replies.
    Checking with local inspectors and building code officials. I will post the information.
  5. #5
    Join Date
    Nov 2009
    Moore, OK
    Posts
    432
    Quote Originally Posted by jumper View Post
    Good find.
    8.6.5.1.1 Sprinklers shall be located so as to minimize obstructions to discharge as defined in 8.6.5.2 and 8.6.5.3, or additional sprinklers shall be provided to ensure adequate coverage of the hazard.
    8.6.5.2.1.3* Unless the requirements of 8.6.5.2.1.4 through 8.6.5.2.1.9 are met, sprinklers shall be positioned away from obstructions a minimum distance of three times the maximum dimension of the obstruction (e.g., structural members, pipe, columns, and fixtures). The maximum clear distance required shall be 24 in. (609 mm) in accordance with Figure 8.6.5.2.1.3.
    Out of curiousity, would the fan blades be considered part of the obstruction, or just the housing/motor unit?
    -Mark
  6. #6
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    1,751
    Fire Code for Sprinklers: 2007 NFPA 13, 8.10.7.2.1.7
    Disregard fan blades where plan view of fan is at least 50% open, motor housing is the 4 times rule
    Roger Ramjet NoFixNoPay
Posting Permissions
  • You may not post replies
  • You may not edit your posts