New Voltage Drop Situation

Status
Not open for further replies.
I'm planning a 4-way lighting system for pathway garden lights. The line and load sides are ~250' apart. The load is going to be a 120v/500 watt transformer for low voltage lights.
My calculation for VD is 250', 15A, 115v using #12 is 12.9%. If I were to #6 I could get the VD down to 3.2%.
I don't want to us 500' of #6.
Should I consider using a buck boost transformer.
Any suggestions world be helpful
 