Closed Thread
Page 3 of 7 FirstFirst 1 2 3 4 5 ... LastLast
Results 21 to 30 of 69
Thread: working live on electrical systems
  1. #21
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,137
    Quote Originally Posted by the blur View Post
    All I see is legal manipulating to shift blame away from the electrical contractor...... who should know better, and take responsibility for his actions.
    Actually the owner of the system is shifting blame to the EC, who should know better if they had the required training to be "qualified" per 70E and OSHA. In the case of the OP the EC did either not know better or was ignoring the requirements on purpose. The OP's company has arc flash labels and PPE requirements posted on the breaker and the EC ignored them and was racking the breaker without any PPE.
    case in point, a 480/277v 600amp service does not have an arc flash label. So the above laws say, the electrician can become a complete moron, and not assume he's opening a dangerous panel, when he should know, any 480v panel has enough energy to do major damage.
    No, if the panel in your example is not labeled the owner has to provide the info needed for the EC to make the assesment required by either doing an arc flash analysis or apply the tables if they can be used, which would need to be determined by the EC using the info provided by the owner (OCPD info and available fault current)
    "Information about the employer’s installation that the contract employer needs to make the assessments required by Chapter 1"
    It sounds like you could really use some training yourself and stop being one of those guys trying to fight the system. Arc flash regulations are not going away, they are in place to protect people from serious injuries, 4-5 people a day are sent to burn centers from arc flash indicents, you ever been in a burn unit? I have, it is hell on earth.
  2. #22
    Join Date
    Aug 2007
    Denver CO
    Posts
    142
    Quote Originally Posted by zog View Post
    And you would lose, it happens all the time. Being licensed has nothing to do with being "qualified" or safe.
    In order to sit for licenseure, you must be first qualified. Once you are licensed by a state (government) you take legal responsibility for your actions like it or not.
  3. #23
    Join Date
    Aug 2011
    cyberspace
    Posts
    160
    Mr. Zog,
    On your course of thinking, or logic, every home owner needs 70E training in order to hire a licensed electrician.
    also, (your logic), every business owner, no matter how small or large, should be trained in electrical, plumbing, HVAC, property management, etc, etc, etc, rather than running their own "expertise", which is obviously not electrical work. Even the chinese restaurant owner should be trained in 70E, so the electrician can fix their wok.
    This is really an embarrasment to the profession of EC.
  4. #24
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    11,948
    I don't agree with the owner being responsible for contractors following safe practices whether it be the use of fall arrest gear or electrical protective gear, or whatever. They called a professional to do a job and expect them to know how to do it - including using safe work practices.
    A big difference for any service company that performs work on the owners property and other companies is the fact you are on someone elses property. If you take your car to a repair shop - how can you be responsible for a technicians failure to follow safe procedures done in their own shop? Now if they come to your place to work on your car it gets complicated, even though they are doing same work. Makes a great breeding ground for legal disputes.
  5. #25
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,137
    Quote Originally Posted by kenaslan View Post
    "Qualified" as defined by the NFPA 70E (And OSHA, which has the same requirements). In this sense it has nothing to do with being an electrician.
    According to the NFPA 70E, a “Qualified Person" is one who is trained and knowledgeable of the construction and operation of the equipment or the specific work method, and be trained to recognize the hazards present with respect to that equipment or work method.
    Such persons shall also be familiar with the use of the precautionary techniques, personal protective equipment, insulating and shielding materials, and insulated tools and test equipment. A person can be considered qualified with respect to certain tasks but still be unqualified for others.
    An employee that is undergoing on the job training and who, in the course of such training, has demonstrated the ability to perform duties safely at his or her level of training and who is under the direct supervision of a qualified person shall be considered to be a qualified person for the performance of those duties.
    In addition, to be permitted to work within the limited approach of exposed energized conductors and circuit parts the person shall be trained in all of the following:
    Qualified employees shall be trained and competent in:
    •The skills and techniques necessary to distinguish exposed live parts from other parts of electric equipment
    •The skills and techniques necessary to determine the nominal voltage of exposed live parts
    •The minimum approach distances specified in this section corresponding to the voltages to which the qualified employee will be exposed, and,
    •The decision making process necessary to determine the degree and extent of the hazard and the personal protective equipment and job planning necessary to perform the task safely
    A few notes to add to the 70E definition.
    •Only the employer can deem an employee qualified after they have had the proper training and have demonstrated profinency using the skills and method learned.
    •There is no such thing as NFPA 70E certification, going to a training course does not make an employee qualified.
    •The most misunderstood part of the "qualified" term is that it is all emcompassing, you are "qualified" to work on a specific type or piece of equipment.
    •Neither a J-card, a masters license, or an engineering degree make you a "qualified person"
    •The word "electrician" is not anywhere in the definition of a "qualified person" meaning these rules apply to all employees and you dont have to be an electrician to be "qualified"
  6. #26
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,137
    Mr. Zog,
    No, they just need to ensure the contractor they are hiring is qualified, and in the OP the EC they hired obviously was not.
  7. #27
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,137
    Quote Originally Posted by kwired View Post
    Which in the OP's question was obviously not the case.
    You have it 100% backwards, if you take your car to the repair shop they don't let you in the garage area under the car (Or are not supposed to anyways, I usually ask if I can see what they found) because if the car falls on you they could be held liable.
  8. #28
    Join Date
    Aug 2011
    cyberspace
    Posts
    160
    Mr. Zog,
    My meter fails while testing panel voltage. I had it on the wrong setting, the meter blows up, and causes a flash. I'm qualified, & I'm burnt.
    Now I get to sue the home owner or building owner because my meter failed.
    Your obviously OK with this logic, and will defend it till the very death, because the laws are written and in stone, even though they are WRONG.
    One day 70e will be overturned, or completely re-written.
    John Stossel just did a show, where he proved everyone in the county is breaking some obsure law they don't know about, and this 70e falls into this relm.
  9. #29
    Join Date
    Feb 2003
    Wisconsin
    Posts
    7,948
    What do you find in NFPA70E that has increased a property owners exposure to being sued?
    Over the past 40 years we have dealt with OSHA rules for employers in regards to Hazardous Material handing, fall protection, LOTO, ergonomics, and so on, so why is the 'current' focus on electrical work any different.
    Just because you can, doesn't mean you should.
  10. #30
    Join Date
    Aug 2011
    cyberspace
    Posts
    160
    Because the EMPLOYER can be a contractor, or a property owner hiring a "professional". Mrs. Jones hires an EC. Is Mrs Jones the EMPLOYER of record ???
Closed Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts