    Art 210.63 requires recept's (usually GFIs) not to be installed on the load side of the disconnect. The wording here confuses me since it makes me wonder if tapping the line side is OK. Problems I see there are putting a 20 A recept on a twenty A circuit might lead to nuisance tripping of the supplying breaker, and could you even put a 20 A recept on a larger circuit? I would think you couldn't. Does this requirement point to something I'm missing, or does it really make sure you don't tap the disconnect at all?
    Thanks for all info.
  2. #2
    Join Date
    Nov 2003
    Roanoke, VA.
    Posts
    4,314
    Quote Originally Posted by jimalex View Post
    I'm sure the intent was not to allow someone to tap a receptacle to the load side of the disconnect because there usually is no grounded conductor available (neutral). only a equipment ground which cannot be used as a neutral.
  3. #3
    Join Date
    Apr 2012
    Burlington NC, USA
    Posts
    6
    Usually I pull a 20 AWG hot and neutral in the pipe with the circuits supplying the equipment, adjust pipe and wire sizes accordingly, and nipple off the disconnect to set the GFI. I just wanted to make sure there weren't any circumstances allowing me to use the line side of the disconnect, for say a 40 amp 3 phase circuit, so i wouldn't have to pull a hot wire, which would allow for not derating the conductors since the neutral wouldn't be counted as a current carrying conductor (310.15.B.5.(a) ). I just can't think that a 20 A recepticle on a 40 A circuit breaker is going to be legal. So, I guess, why wouldn't the code just say "don't tap the line or load side of a disconnect for a service outlet"?
  4. #4
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,193
    A 20 amp receptacle installed on a 40 amp circuit is not code compliant, but if I size the feeder to the A/C disconnect correctly for both the A/C unit and the receptacle and follow the feeder tap rules in 240.21(B) I could tap off the line side of the A/C disconnect and supply a receptacle provided that I protect the receptacle with a properly sized OCPD. You would also need to bring in a neutral with the feeder conductors.
    Chris
  5. #5
    Join Date
    Apr 2012
    Burlington NC, USA
    Posts
    6
    Thanks, Chris. Just what I needed to see.
    Jim
  6. #6
    Join Date
    Nov 2004
    WA
    Posts
    2,128
    I say let the hvac installer install it. It seems they know more than we do, and are telling customers they are allowed to do the electrical portion of the install any how........ At least in my area. Strangly enough, they violate code each time!
    Lost for words
  7. #7
    Join Date
    Apr 2012
    Burlington NC, USA
    Posts
    6
    Quote Originally Posted by resistance View Post
    Hah! in my experience, EVERYBODY who isn't an electrician thinks they do better electrical work than we do!
  8. #8
    Join Date
    Apr 2009
    Clarkesville, Georgia
    Posts
    2,028
    Don't tap the load side because the guy working on the unit may need to plug into recep but have power off the unit while he's working.
  9. #9
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,046
    We use CHs DPU222RGF. New models have the required WR device. Pull two, circuits, one for the A/C and one for the device. If you are on a low budget it can be one of the required two outside recepts.