    Derating Parallel conductors in a raceway

    Raceway:
    I have a 3” raceway (part pvc and part aluminum) that has (8) 3/0 thhn copper conductors. (2 sets of a,b,c and 2 neutrals).

    I’m looking at table 310.15(B)(2)(a) and wondering if I should adjust by 80 (6 conductors (the 2 sets of a,b,c)) or if I should adjust by 70 (all 8 wires(the 2 sets of a,b,c and the 2 neutrals)).

    Assuming that’s the correct table, I guess it boils down to whether or not the neutrals are considered ‘current-carrying conductors’ – are they?

    Setup:
    GA Power Transformer is feeding a 480/277 3/0, 4-wire, 1200amp main breaker via (3) of the raceways described above.

    What would be the adjusted rating of the main breaker in this scenario?

  2. #2
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,851
    This section defines when it it is a CCC or not.


    310.15(B)(4) Neutral Conductor.
    (a) A neutral conductor that carries only the unbalanced
    current from other conductors of the same circuit
    shall not be required to be counted when applying the provisions
    of 310.15(B)(2)(a).
    (b) In a 3-wire circuit consisting of two phase conductors
    and the neutral conductor of a 4-wire, 3-phase, wyeconnected
    system, a common conductor carries approximately
    the same current as the line-to-neutral load currents
    of the other conductors and shall be counted when applying
    the provisions of 310.15(B)(2)(a).
    (c) On a 4-wire, 3-phase wye circuit where the major
    portion of the load consists of nonlinear loads, harmonic currents
    are present in the neutral conductor; the neutral conductor
    shall therefore be considered a current-carrying conductor.
    "Electricity is really just organized lightning." George Carlin


    Derék

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    12,764
    If I did my math correctly, you are in trouble either way.
    If you are supplying a 1200 main breaker, your total conductor ampacity must be at least 1200 amps.
    Parallel 3/0 (225 x 2 x .8) in 3 conduits comes up to 1080 amps

    In direct answer to your question, the neutral being a ccc depends on 310.15(B)(4) and if a majority of your load is linear or non-linear. We would need to know a little more about the load to determine. (Normally the neutral does not count on services)

    (jumper answered that part as i was typing, sorry)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    13,069
    Quote Originally Posted by StanRob View Post
    ...

    What would be the adjusted rating of the main breaker in this scenario?
    Well hopefully the main breaker is adjustable.

    3 sets of 4x3/0 THHN Cu with a 75°C terminal temperature limitation [110.14(C)] would put you at 400A max per conduit x 3 = 1200A. That's before ampacity adjustments. Using full ampacity rating, you have 225A x 6 = 1350A. At the very least you have to derate 80% for ccc's. That puts you at 1080A...
    I'll never get there. No matter where I go, I'm always here.

  5. #5
    Join Date
    Apr 2012
    Location
    Gainesville,GA,USA
    Posts
    2
    Thank you all very much for the quick and thorough replies!