Page 1 of 2 12 LastLast
Results 1 to 10 of 14
Thread: 10 foot tap rule
  1. #1
    Join Date
    May 2007
    Bay Area
    Posts
    24
    10 foot tap rule
    the feed is 225 tap main.
    want to add two panels down stream within 10', they are both rated at 225. Is this allowed and what size wire for the taps.
    Could some one please explain the math of the tap rule(s).
    Thanks,
    j9
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,152
    Quote Originally Posted by j9DuBois View Post
    Thanks,
    j9
    The main feed is a tap and you want to tap it?
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Feb 2003
    Ohio
    Posts
    1,013
    I'm with Jumper, a little more info is needed. Also, when you use the 10 foot tap rule remember this is wire length not if the equipment is within that distance.
    Pete
    Experience is something thats gained shortly after you really needed it.
  4. #4
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Thanks,
    j9
    First thing we need to know is what you are planing to connect to and then we can figure out if the tap rules even apply.
    Are you connecting to service conductors or a feeder?
    What size wires would you be connecting too?
    If it is a feeder what size breaker or fuse is protecting it?
  5. #5
    Join Date
    Feb 2003
    Illinois
    Posts
    23,355
    I have no idea what a tap main is. Can you explain it?
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  6. #6
    Join Date
    Jan 2009
    Posts
    14,152
    Quote Originally Posted by don_resqcapt19 View Post
    Hey, didn't I ask that already? Wait your turn.
    Derek
  7. #7
    Join Date
    May 2007
    Bay Area
    Posts
    24
    tap rule
    ok, more info.
    Nothing yet exists.
    There is a main ( I don't know what athe ampacity is) So from what Info I could gather one panel is going to be 225 amps and then the other is going to be tapped off of the first one also at 225 amps. I think we would go with 4/0, (foreman says 3/0) from the main and then the tap would have what size wire? the same?
    Could someone exlain what "the rating of the oc device on the line side of the tap conductors shall not exceed 10 times the ampacity of the tap conductor" mean...?does it mean that whatever we tap off the 225 needs to be 22.5 amps or larger?
    thanks.
  8. #8
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,780
    OK, I am still confused. Let’s start here: You say that nothing yet exists, but I infer that there does exist some upstream panel that will be feeding the two new panels you have been discussing. Within that upstream panel, there will be a breaker that will serve the first of your two new panels. What is that breaker’s rating? Next, what is the ampacity of the wire from that breaker to the first panel? If I were designing this setup, my answers to those two questions would be, 225 amps, and 4/0, in that order.
    Part of my confusion is that I think you are using the word “tap” as though it meant the same thing as “connect a wire to.” It does not. Rather, it means something like "connect a smaller wire to a bigger wire." Specifically, when you connect a new wire to an existing wire, you only call it a “tap” if the ampacity of the second wire is lower than the trip rating of the breaker that is protecting the first wire. In other words, if in your situation you have a 225 amp breaker that is protecting a 4/0 wire that serves the first 225 amp panel, and if you connect another 4/0 wire from the first panel to the second panel, then you do not have a “tap” situation. The second wire would be adequately protected by the 225 amp breaker.
    Now, if you wanted to use a smaller wire than 4/0 from the first panel to the second panel, that smaller wire would not be adequately protected by the upstream 225 amp breaker. You are allowed to do that if you follow the tap rules in 240.21. But you are feeding a 225 amp panel, so why would you want to feed it with a wire that does not have the full 225 amp ampacity?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  9. #9
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,780
    I think we would go with 4/0, (foreman says 3/0). . . .
    The foreman is wrong. That is, unless the foreman can produce a calculation that shows that the load is no higher than 200 amps (i.e., the ampacity of a 3/0), then you need a 4/0 to serve the 225 amp panel.
  10. #10
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    If the feeder and all of the panels are rated for 225 amps you wouldn't even need a tap, the tap rule or a main OCPD in the panels. Just use #4/0 for each panel.