How do you calculate arc fault current of a transformer? I believe KVA and transformer impedance are factors in calculation, but not sure how it's done. Would someone give an example? Thanks.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you are asking about the short circuit current, it is the full load amps divided by the impedance (in decimal form, 5% =0.05). This will give you a "infinite bus" value which is the worst case.
 

Ken 6789

Senior Member
Thanks, I meant to say short circuit. I don't know why I was thinking arc.

So is the following correct? 75 KVA = 75,000/240 volts = 312.5 amps. 312.5/.05 = 6,250 short circuit current
 
Last edited:

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do not use the infinite bus method to determine the only short circuit current which will be used when performing an arc flash calculation.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Thanks, I meant to say short circuit. I don't know why I was thinking arc.

So is the following correct? 75 KVA = 75,000/240 volts = 312.5 amps. 312.5/.05 = 6,250 short circuit current

Yes. That's a conservative estimate, assuming there aren't any large motors that would contribute a lot.
 

tkb

Senior Member
Location
MA
Is that for single phase or three phase.

I get 4,009 on a three phase transformer using the Bussman point to point calculations.

AIC.jpg
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Is that for single phase or three phase.

I get 4,009 on a three phase transformer using the Bussman point to point calculations.

AIC.jpg

FWIW,
With the current generation of energy efficient transformers, 5% is a relatively high impedance for a 75kVA 3-ph dry type, and it is extremely high for a utility supplied liquid filled unit (Xcel Energy recommends using 1.6%Z)
 

tkb

Senior Member
Location
MA
Is the result correct in my formula with the parameters that I used?

I am trying to see if I interpreted it correctly and that I wrote the excel formula right.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Is the result correct in my formula with the parameters that I used?

I am trying to see if I interpreted it correctly and that I wrote the excel formula right.


If we assume its a 240V, three phase system, with 5% Z: I get 3608 Amps.

75,000/(240*1.73)= 180 amps.

180/.05 = 3608
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The original posters calculation left out the 1.73 so I assume we are talking about a single phase transformer.
 