Residential UF cable to post light

Status
Not open for further replies.

marmathsen

Senior Member
Location
Seattle, Wa ...ish
Occupation
Electrical Contractor
As per 300.5 column 4 states that minimum burial depth of 12”
Cannot find any exception to say I cannot go with the 12” on UF, just checking if anyone has used this column for UF cable

Thanks


Sent from my iPhone using Tapatalk
Yes you are correct so long as it is 120V, 20A or less, GFCI protected, and isn't under a road or airport runway.

That said, I have troubleshot and repaired A LOT of UF wire over the years. Between shifting ground, roots, shovels, etc. It's just a recipe for disaster. I would strongly recommend using conduit especially if you're only going to be 12" deep.

Rob

Sent from my Pixel XL using Tapatalk
7a5aa9b6b5f9fab9fc6494889cca1d81.jpg
 

jumper

Senior Member
Yes you are correct so long as it is 120V, 20A or less, GFCI protected, and isn't under a road or airport runway.

That said, I have troubleshot and repaired A LOT of UF wire over the years. Between shifting ground, roots, shovels, etc. It's just a recipe for disaster. I would strongly recommend using conduit especially if you're only going to be 12" deep.

Rob

Sent from my Pixel XL using Tapatalk
7a5aa9b6b5f9fab9fc6494889cca1d81.jpg