    Is it OK to install an exterior panel this way?

    A box has been built below this surface mounted 100 A service to enclose circuit conductors that run down the wall to a crawlspace. A few additional circuits enter the back of the box through the wood siding. There is a 3' wide eve at the top of this 8' wall but I imagine this service is exposed to driving rain from time to time. The back of the panel does not appear to be caulked to the wall to prevent water entry.

    [IMG][/IMG]

    This house is wired with Romex cable, but all of the original homeruns were sleeved with 1/2" flexible steel conduit up to the first outlet box. I have never seen anything like this before. I've been asked to upgrade the service to 200 amps. The simplest way to do that would be to shorten the soffit by whatever amount is necessary to accommodate the new panel and hook everything back up more or less the way it is now except that I would use a OH only panel designed to allow circuit entry across the entire bottom of the can. There is a stud bay directly behind this old panel and although it would be a little more difficult I think this whole mess should be replaced with a new semi-flush panel. What would you do?

    [IMG][/IMG]

    Someone ran Carflex under the house with a set of #6 CU conductors with the apparent intension of installing a spa, but then found there was no access to the panel.


    [IMG][/IMG]

    [IMG][/IMG]
    Gary

  2. #2
    Join Date
    Feb 2003
    Location
    San Francisco Southbay
    Posts
    1,635
    As of today NEC 2008 NM cable can not be sleeved in a conduit that is installed outside. But then again the conduit is behind the panel and it would be a call of the AHJ to determine if behind the panel is a damp location.
    Other items that i see that may be an issue is working platform in front of the panel and the FMC is not strapped properly.
    Edward
    Education is a progressive discovery of our ignorance.

  3. #3
    Join Date
    Jun 2007
    Location
    brick nj
    Posts
    170

    Outdoor receptacle

    What is poking out from receptacle on right. Looks very naughty. Nice picture.

  4. #4
    Join Date
    Feb 2003
    Location
    California
    Posts
    122
    Quote Originally Posted by highvolts582 View Post
    What is poking out from receptacle on right. Looks very naughty. Nice picture.
    There are two small low power wall warts plugged into the receptacle. They are being used to power two nearby water softener controllers.
    Gary

  5. #5
    Join Date
    Feb 2003
    Location
    California
    Posts
    122
    Quote Originally Posted by edward View Post
    As of today NEC 2008 NM cable can not be sleeved in a conduit that is installed outside. But then again the conduit is behind the panel and it would be a call of the AHJ to determine if behind the panel is a damp location.
    Other items that i see that may be an issue is working platform in front of the panel and the FMC is not strapped properly.
    The condition of the FMC is quite good which would seem to indicate that the interior of the box has remained dry. I hadn't really noticed the working space issue. Thanks for pointing that out!
    Gary

  6. #6
    Join Date
    Jun 2007
    Location
    brick nj
    Posts
    170

    Insulation

    Quote Originally Posted by gary View Post
    There are two small low power wall warts plugged into the receptacle. They are being used to power two nearby water softener controllers.
    Is the insulation of the wall warts rated to be exposed to sun light is where I was going with that one.

  7. #7
    Join Date
    Oct 2006
    Location
    Litchfield, CT
    Posts
    8,622
    I have no problem with this install, I'm doing a job now where I have no choice but to run all my new NM circuits down the existing outside wall of a garage to be boxed in at a later date by the carpenters....
    "Electricity is actually made up of extremely tiny particles called electrons, that you cannot see with the naked eye unless you have been drinking."

  8. #8
    Join Date
    Feb 2003
    Location
    NE Arkansas
    Posts
    2,222
    I believe you're actually required to maintain a space between the panel and the wall when you surface-mount it in a wet location. That would ban your caulk idea.

  9. #9
    Join Date
    Feb 2009
    Location
    Durango, CO
    Posts
    3,142
    Quote Originally Posted by stickboy1375 View Post
    I have no problem with this install, I'm doing a job now where I have no choice but to run all my new NM circuits down the existing outside wall of a garage to be boxed in at a later date by the carpenters....
    True dat! And in both your case and/or the OP's, if everything is boxed in why bother with the flex?
    If Billy Idol or John Denver is on your Ipod go and re-evaluate your life.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •