    Westinghouse breakers in federal Pacific panel

    Has anyone ever used any westinghouse breakers in a federal pacific panelboard. I have a project with a FP panelboard and my vendor is telling me they sell westinghouse for these.

  2. #2
    Join Date
    Jul 2005
    Location
    northern new jersey
    Posts
    220
    I don't think they fit. I would throw this panel in the garbage.
    Here's a company that does sell listed replacement
    http://products.connecticut-electric...010%7D&cpage=1
    Keep you insurance up to date!

  3. #3
    Join Date
    Sep 2011
    Location
    WI
    Posts
    77
    Quote Originally Posted by shaw0486 View Post
    Has anyone ever used any westinghouse breakers in a federal pacific panelboard. I have a project with a FP panelboard and my vendor is telling me they sell westinghouse for these.
    I remember back late 70's, early 80's, some private labeling of bolt-on breakers between FPE and Westinghouse was going on. Depending on the type of panel and breakers, factory built panels could have one or the other.

  4. #4
    Join Date
    Feb 2012
    Location
    Kansas
    Posts
    388
    Quote Originally Posted by shaw0486 View Post
    Has anyone ever used any westinghouse breakers in a federal pacific panelboard. I have a project with a FP panelboard and my vendor is telling me they sell westinghouse for these.
    given the option, i would ask the vendor for a different panelboard to install
    Hard work never hurt anyone....but why risk it

  5. #5
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    5,819
    We went around the area and replaced FPE breakers that were subject to recall back in the 80s ?? We replaced them with Westinghouse.
    Tom
    TBLO

  6. #6
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    3,233
    UL letter to Westinghouse/C-H for breaker replacements. Now this letter doesn't include clasified breakers that they offer.
    Attached Images Attached Images

  7. #7
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    3,233
    Quote Originally Posted by templdl View Post
    UL letter to Westinghouse/C-H for breaker replacements. Now this letter doesn't include clasified breakers that they offer.
    These are the C-H classified breakers. This is all I got.
    Attached Images Attached Images  