I was told that conduits can be run vertical in a bloch wall through the block openings. Can MC be run this way although I guess supporting it would be an issue?
II. Installation
330.10 Uses Permitted.
(A) General Uses. Type MC cable shall be permitted as follows:
(1) For services, feeders, and branch circuits
(2) For power, lighting, control, and signal circuits
(3) Indoors or outdoors
(4) Exposed or concealed
(5) To be direct buried where identified for such use
(6) In cable tray where identified for such use
(7) In any raceway
(8) As aerial cable on a messenger
(9) In hazardous (classified) locations as permitted
(10) In dry locations and embedded in plaster finish on brick or other masonry except in damp or wet locations
Is it in a dry location?
Yes. But how would you support the vertical MC in a block wall? THanks.
I was told that conduits can be run vertical in a bloch wall through the block openings. Can MC be run this way although I guess supporting it would be an issue?