Originally Posted by
jim dungar
...
Your transformer bank output is 43.3kVA 3-phase, personally, I think this is a little small for staring a 40HP submersible pump.
That jumped right out at me too!
altarengineering,
Even if you are using a VFD for this pump you are a little too small; assuming 480V, a 45kVA transformer is 54A and you only have 43.3kVA so that makes it 52A, a 40HP motor is 52A FLC. Any voltage drop down the well and you are sunk but if you are starting it with anything other than a VFD, fuggedaboudit. It likely won't even finish accelerating.