Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Ok, let's saya spec limits (3) cicruits to a conduit and says all homeruns must be #10 wire. If you have say (12) circuits in an area about 150' away why would you ever run a homerun out to that location? Would'nt you run the homerun 10-20' feet out then run the #12's to the location.......keeping the homeruns as short as possible? THanks.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If I had 12 circuits 150 feet away I believe I would run a feeder and set a sub panel.

I think you are trying to cheat here. A homerun is the wire between the first device and the panel. Setting a JB and getting by that way is not the intent of what is being specified. The purpose of a #10 homerun is for Voltage Drop. To do what you suggest would not help with this issue.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
If I had 12 circuits 150 feet away I believe I would run a feeder and set a sub panel.

I think you are trying to cheat here. A homerun is the wire between the first device and the panel. Setting a JB and getting by that way is not the intent of what is being specified. The purpose of a #10 homerun is for Voltage Drop. To do what you suggest would not help with this issue.

Besides setting a sub panel, if you ran #10 you would almost have to transition to #12 to land on some devices wouldn't you?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No more than three circuits to a conduit seems to deal with derating issues (maybe). The #10 AWG conductors as Dennis suggested are for voltage drop. 150' homeruns are pretty common in commercial applications when panels are located in a central electric closet.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Yes, the receptacles would be wired with #12's but can't that branch circuit be run close to the panel to a box then splice with #10's for the dhort home run. My question is why would the #10 homerun have to be run out(about 150') to the area near the receptacles? Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, the receptacles would be wired with #12's but can't that branch circuit be run close to the panel to a box then splice with #10's for the dhort home run. My question is why would the #10 homerun have to be run out(about 150') to the area near the receptacles? Thanks.

Dennis answered that question in post #2. You would use larger conductors for voltage drop compensation.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Dennis answered that question in post #2. You would use larger conductors for voltage drop compensation.

Yes, but I am saying that I think #12's would be fine to run 150'.... i think?? Hence my question about a short homerun..and no need to run it 150'
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes, but I am saying that I think #12's would be fine to run 150'.... i think?? Hence my question about a short homerun..and no need to run it 150'


It doesn't matter what you think the engineer specified it so running a short piece of #10 will not satisfy his request, IMO.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What do you base your comment on that #12 is okay. If there is a 20 amp load on the circuit then a #12 would not be okay. What is the circuit feeding?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, but I am saying that I think #12's would be fine to run 150'.... i think?? Hence my question about a short homerun..and no need to run it 150'


Well if you're in a position to perform value engineering and save some money then do it. But if I'm writing the spec for 3 circuit, #10 homeruns in a raceway then I would not accept anything less.

Just curious, what method are you using to determine that the #12's may be sufficient for a 150' run? I'm not saying that they aren't just wondering how you would go about determining that.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
It doesn't matter what you think the engineer specified it so running a short piece of #10 will not satisfy his request, IMO.


How would that not satisy his request? Because a "homerun" is from the last device? From what I have seen, and the engineer is okay with it in the past, you can run from the "last device" to a homerun box then to the panel. So like I was saying that homerun box would be right outside the electrical closet.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Well if you're in a position to perform value engineering and save some money then do it. But if I'm writing the spec for 3 circuit, #10 homeruns in a raceway then I would not accept anything less.

Just curious, what method are you using to determine that the #12's may be sufficient for a 150' run? I'm not saying that they aren't just wondering how you would go about determining that.

MH vd calculator but I think I entered wrong.
 

JES2727

Senior Member
Location
NJ
OK. But nobody agrees with you.
What is the point of a #10 home run if it changes to #12 right outside the closet? Why bother with #10 at all?
 

DetroitEE

Senior Member
Location
Detroit, MI
How would that not satisy his request? Because a "homerun" is from the last device? From what I have seen, and the engineer is okay with it in the past, you can run from the "last device" to a homerun box then to the panel. So like I was saying that homerun box would be right outside the electrical closet.

I sincerely doubt that would be acceptable to the engineer that specified this. You can't just put a jbox 10' from the panel and say that after that 10', it's no longer a home run. The intent is obviously to use #10s for the majority of the run length in order to minimze voltage drop.

I would caution you to avoid just assuming the voltage drop will be "fine" at 150'. It only takes 7 amps at 150' with #12s to exceed 3%.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I sincerely doubt that would be acceptable to the engineer that specified this. You can't just put a jbox 10' from the panel and say that after that 10', it's no longer a home run. The intent is obviously to use #10s for the majority of the run length in order to minimze voltage drop.

I would caution you to avoid just assuming the voltage drop will be "fine" at 150'. It only takes 7 amps at 150' with #12s to exceed 3%.

Yes I just saw that on the calculator.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Adding to post #14 and #15, you would gain practically nothing by doing as you suggest other than pulling the wool over someones eyes by making them think you had a #10 home run from the general area of the load.
If you truly had a 20 amp load, the voltage drop on a #12 for the full 150 ft would be 11.88 volts, far in excess of the 3.6 desirable. If you just ran the #10 for 20 ft and then changed to #12 you would still have 10 volts drop.
With a full 20 amp load, even a #10 for the full length gives you a 7 volt drop.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I sincerely doubt that would be acceptable to the engineer that specified this. You can't just put a jbox 10' from the panel and say that after that 10', it's no longer a home run. The intent is obviously to use #10s for the majority of the run length in order to minimze voltage drop.

I would caution you to avoid just assuming the voltage drop will be "fine" at 150'. It only takes 7 amps at 150' with #12s to exceed 3%.

So if you have a circuit with say (6) 20a general receptacles feeding computer, printers etc. I would say each might draw 1-2 amps. So then #10 homerun....
 

DetroitEE

Senior Member
Location
Detroit, MI
So if you have a circuit with say (6) 20a general receptacles feeding computer, printers etc. I would say each might draw 1-2 amps. So then #10 homerun....

Correct, I would definitely want those #10s for the home run for a circuit feeding workstations that contain computers and printers.
 