Solar with a Standby Generator

Status
Not open for further replies.

mkgrady

Senior Member
Location
Massachusetts
I’m wiring a whole house standby that currently has a solar system. The solar circuit connects to the house service at the 200 amp mater/main breaker (load side). The connection is made with a tap splice onto the 4/0 aluminum SER. From there the SER runs to the house panel.

The 200 amp ATS will mount outside next to the meter/main. My question is about where this solar connection should be when the generator wiring is complete. If the tap remains as is the solar system will be feeding into the generator output during an outage. Is this a problem? Or will it just synch up with the generator output like it does when POCO power is being used.

These questions probably tell you how little I know about solar power. Hopefully I’m not the only one on here that can get something out of this question.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I’m wiring a whole house standby that currently has a solar system. The solar circuit connects to the house service at the 200 amp mater/main breaker (load side). The connection is made with a tap splice onto the 4/0 aluminum SER. From there the SER runs to the house panel.

The 200 amp ATS will mount outside next to the meter/main. My question is about where this solar connection should be when the generator wiring is complete. If the tap remains as is the solar system will be feeding into the generator output during an outage. Is this a problem? Or will it just synch up with the generator output like it does when POCO power is being used.

These questions probably tell you how little I know about solar power. Hopefully I’m not the only one on here that can get something out of this question.

Your genset must be down stream from the solar.
 

mkgrady

Senior Member
Location
Massachusetts
Your genset must be down stream from the solar.

Are you saying the solar connection needs to remain where it is? If it stays on the load side of the main at the meter/main and upstream of the Ats the generator output will never see the solar output. That seems right to me. Is it?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Can’t say that I understand. Can you elaborate?
The solar connection needs to be outside (on the utility side) of the transfer switch. Yes, this means that the solar will not run when the grid is down, but connecting it inside the transfer switch would enable the PV to backfeed the generator when the loads are drawing less than what the PV is producing, which would be very bad for the generator.
 

mkgrady

Senior Member
Location
Massachusetts
The solar connection needs to be outside (on the utility side) of the transfer switch. Yes, this means that the solar will not run when the grid is down, but connecting it inside the transfer switch would enable the PV to backfeed the generator when the loads are drawing less than what the PV is producing, which would be very bad for the generator.

Thanks for that response. Very helpful.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
That is assuming that the generator frequency and voltage are stable and accurate enough to qualify to the inverter and that its output impedance is low enough to satisfy the anti islanding schemes. In many cases the grid tied inverter simply will not run when connected to the generator.
If the inverter had a mode that relaxes the "grid" specs to work with a generator, then you risk the problem ggunn describes.

Sent from my XT1585 using Tapatalk
 
That is assuming that the generator frequency and voltage are stable and accurate enough to qualify to the inverter and that its output impedance is low enough to satisfy the anti islanding schemes. In many cases the grid tied inverter simply will not run when connected to the generator.


Sent from my XT1585 using Tapatalk

I agree and doubt this is actually an issue. Even if it did initially synch, and then power production exceeded usage, I think voltage and or frequency would rise and the inverter would shut down then. That said, I of course wouldn't do it as a professional.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
Thanks for that response. Very helpful.

We have had customers who got concerned about the PV not continuing to run during an outage when they are using the generator, and it is possible to design a PV system that will, but it's expensive. If outages are relatively rare and short-lived, the contribution to their bottom line from the PV system during outages is minuscule.
 