Page 2 of 3 FirstFirst 123 LastLast
Results 11 to 20 of 27

Thread: UL Listing Requirements on 12V LED Fixtures

  1. #11
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,559
    We could argue it but I don't buy it either but NC , I believe , used that article as its argument.

    410.6 states all luminaires and lampholders shall be listed as well as what Bob stated.

  2. #12
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,950
    Quote Originally Posted by Dennis Alwon View Post
    We could argue it but I don't buy it either but NC , I believe , used that article as its argument.

    410.6 states all luminaires and lampholders shall be listed as well as what Bob stated.
    Dennis, if 110.3(B) was in fact meant to require all equipment to be listed all of the .6 sections of the NEC that require listed equipment would be moot.

    Chris

  3. #13
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,559
    Quote Originally Posted by raider1 View Post
    Dennis, if 110.3(B) was in fact meant to require all equipment to be listed all of the .6 sections of the NEC that require listed equipment would be moot.

    Chris
    or redundant

  4. #14
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,950
    Quote Originally Posted by Dennis Alwon View Post
    or redundant
    Exactly, that is my point.

    110.3(B) is meant to clearly show that requirements that may not be in the NEC but are part of the listing instructions of listed equipment are required to be followed.

    Chris

  5. #15
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,212
    Quote Originally Posted by Dennis Alwon View Post
    Well I knew someone would argue that however
    Of course as it seems a very unusual position.

    IMPO there is nothing in 110.3(B) that requires anything to be listed.

  6. #16
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    8,035
    Quote Originally Posted by iwire View Post
    Of course as it seems a very unusual position.

    IMPO there is nothing in 110.3(B) that requires anything to be listed.
    I agree; however, I can easily see how it could be interpreted that way by the opening words of that section as Dennis presented.

    "listed or labeled equipment shall be installed and used in accordance with"....

    These words could be considered definitive, binding and inclusive as written.
    The immediate quote above is from my wife, who has a MA in English.
    "Electricity is really just organized lightning." George Carlin


    Derék

  7. #17
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,212
    Quote Originally Posted by jumper View Post
    I agree; however, I can easily see how it could be interpreted that way by the opening words of that section as Dennis presented.

    "listed or labeled equipment shall be installed and used in accordance with"....



    The immediate quote above is from my wife, who has a MA in English.
    Only if you choose to stop reading the sentence before it is done.

  8. #18
    Join Date
    Jun 2012
    Location
    United States
    Posts
    1

    Listing requirements for 12v LED Strip Lights


  9. #19
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,559
    Quote Originally Posted by oHall View Post
    NC has a list if NRTL's that it will accept. Check with your state to insure that there is not a separate list from the one posted.

  10. #20
    Join Date
    May 2012
    Location
    United States
    Posts
    10
    Novice question, but what is NC?
    Also, can anyone point me in the direction to check with my state (Florida) on their NRTL? I've checked OSHAs list, just want to see if FL adds any. :-)

Tags for this Thread