Did we ever hear what size wire the plans call for? Most jobs I've bid tell you the wire size somewhere.
Lou (wannabe economist)
If you relentlessly pursue perfection, you will eventually catch excellence.
I was just awarded a job. The plans may be complete next week.
Tom
TBLO
the prints will call for two #6 and #8 ground.
i haven't drawn them yet.
it was my shortfall, i didn't realize the repeaters would pull that much.
i was figuring a nominal 180 watts per device, a quad would give 360 watts, or three amps.
i am now the proud owner of six rolls of #6 simpull, and three rolls of #8 green simpull.
$2,200 or so.
next time, i'll clarify something like that.... 'eh, it's only THREE OUTLETS, not even something to consider.... ;-)
“Give a person a fish and you feed them for a day;
teach that person to use the Internet and they won't bother you for weeks.”
If this is a 20 amp circuit and conductor size is increased to #6 for voltage drop purposes then the equipment grounding conductor also needs to be increased to #6.
If this is a 60 amp circuit using 6 AWG conductors - the equipment grounding conductor can be 10 AWG.
Just doesn't quite sound right does it? But that is what code says.
A code compliant way to use the 10 AWG EGC is to run a feeder to near the outlet with 10AWG EGC. Then run shorter 20 amp branch circuit to the outlet with smaller conductors.