And if OP runs a 6 AWG feeder instead of a 6 AWG branch circuit protected at 20 amps table 250.122 says minimum size equipment grounding conductor is 10 AWG. A loop hole to get around using a #6 EGC is to make the majority of the run a feeder and it is code compliant to use 10 AWG instead of 6 AWG, yet your conductors are effectively supplying the same thing.
well, unmarred by facts, my first thought was that the EGC needed to be sized to match the overcurrent
device, at 20 amps. the fact that i can use the emt as a ground and not even use a ground wire......
my electrical engineer, who gets to bless the drawing i do with his signature, when i spoke with him, whining
about having to pull #6, i asked him what size ground do i pull... and he said.... #8.....
and that is where that is at. i'm open to any opinions to the contrary....
thanks for taking the time to reply.
“Give a person a fish and you feed them for a day;
teach that person to use the Internet and they won't bother you for weeks.”
now, how might i make a pair of #6 wires, serving a quad outlet 500' away, be a feeder? by setting a panel with
a single circuit breaker in it 3' from the quad?
interestingly, there is not a single branch circuit in this facility that has larger than #10. the dock light plugs,
which run 300' from the panels, are #12.
building is 6 years or so old.
Last edited by Fulthrotl; 05-30-12 at 11:58 PM.
“Give a person a fish and you feed them for a day;
teach that person to use the Internet and they won't bother you for weeks.”
(B) Increased in Size. Where ungrounded conductors are increased in size,
equipment grounding conductors, where installed, shall be increased in size
proportionately according to the circular mil area of the ungrounded conductors."
so, on this 110 volt single circuit, is there any reason i have to pull a ground wire?
or is the EMT a sufficient ground path? it's a 3/4" emt conduit, with, at this point,
two wires in it.
Last edited by Fulthrotl; 05-31-12 at 12:22 AM.
“Give a person a fish and you feed them for a day;
teach that person to use the Internet and they won't bother you for weeks.”
simple fatigue, mostly. i decided to sleep in till 4:30 am today.
i was cranky yesterday....
lessee... #6 is $250 or so a spool... three spools is $750.
and all the conduit and box is caddy clipped or screwed to building
steel.
yeah, i think it'll be grounded. delete ground wire.....![]()