    Quote Originally Posted by PEDRO ESCOVILLA View Post
    because exit lights with battery back up are considered "emergency systems", or part of an emergency system, they have to comply with 700.12.
    And part F of that section addresses undividual units which is your typical self contained egress lighting unit.
    Essentially each unit is its own system as the emergency supply power comes from within each unit. Not the same thing as a central supply and running circuits out from there to where illumination is needed.
  2. #22
    Join Date
    Feb 2003
    Massachusetts
    Posts
    45,321
    Quote Originally Posted by kwired View Post
    It is exactly the same as any emergency supply and the same rules apply on the load side of the supply. If you do a remote lamp off of the unit equipment which not unusual it is an emergency circuit
  3. #23
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    12,029
    Quote Originally Posted by iwire View Post
    I agree, if you have self contained unit it is a system of its own, if you have remote lamps they are part of that system, but are not related to the separate self contained system in the next room.