Thread: Gate Power with 1700 Foot Driveway

  1. #11
    Join Date
    Dec 2010
    Location
    -
    Posts
    1,505
    Battery power gate controller (in case power goes out) with a trickle charger. Run a #8 to the gate in the conduit previously installed. Maybe run a light or two also at the gate...

  2. #12
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    1,181
    My thinking follows A/A, Ron, George B. Figure out the customers' wants - not their needs. I'm guessing anyone with a 1/4 mile driveway can afford what they want. But maybe not - perhaps shaving a few bucks matters to them. Just have to be careful on how you ask. Just the way the questions are phrased can push them one way or another.

    If I had to guess, they will want the most cost effective system that is close to zero maintenance and utterly reliable. I'd be looking at that conduit and if not available then the service. Anything else is more maintenance and less reliability.

    ice
    Harmless flakes working together can cause an avalanche of destruction

  3. #13
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    1,181
    System is still giving me intermittent fits of editing. (grimace)

    I didn't see Hv's post. If the power is not particularly reliable, they may want a battery back up. But if it is reliable, they may wish to forgo the extra maintenance and use the mechanical disconnect for the few times the power is out. If they let the backup maintenance go and the first tme the power is out is three years later and bats are no good - the backup didn't help much.

    ice
    Harmless flakes working together can cause an avalanche of destruction

  4. #14
    Join Date
    Jun 2009
    Location
    97006
    Posts
    356

    Mighty Mule

    I see lots of these out in the sticks.
    The problem could be if your customer wants and intercom, an alarm and a camera.

    http://www.mightymule.com/

  5. #15
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    48,187
    With 2 AL and a 10 amp load at 240 VAC I come up with less than 5% drop and I doubt the load would be that high. Place a small transformer to get the 120 volts and it's done.

    We can think it to death or just get out an do it. Honestly 1700' is not that far, consider the parking lot lighting at your local shopping plaza.

  6. #16
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    18,064
    If you run power to this area they will want lighting, and receptacles too.

    Down the road they will add some structure that needs power and figure there is power at the gate and it is not too far away next thing you know the feeder you installed is not large enough. If POCO can put in service easily it is worth consideration. Around here montly charge for service would be around $18 even if no power was used. More expensive than replacing batteries every three years but if they want it to be more service free..

    These things are going to require more service than just changing batteries at times so that may not be as big of an issue as some might think.

  7. #17
    Join Date
    Oct 2007
    Location
    British Columbia, Canada
    Posts
    613
    Quote Originally Posted by petersonra View Post
    kick it up to 600V at the house and back down to 120V out at the gate. transformers are a lot cheaper than 3400 feet of wire.
    That's what I was thinking too.

    It's done all the time around here along the railway lines. There's a campground I stay at every summer which has a hiking trail along Canadian Pacific tracks. There are 3 road crossings relatively close together, and I've looked at the layout. There's a 200A meter base at the middle crossing which feeds 120/240 into the cabinet for that crossing plus a pair of 600V xfmrs. At each of the far crossings it's stepped back down to 120/240 (they use the same model xfmr on each end)
    "The Doppler effect means red lights will appear to be green if you drive fast enough..."
    1) Wait for disaster 2) Determine it's not your fault 3) Blackmail the culprit 4) Profit

    Caution: Classless when exhausted from a tough day at work, may attempt to compensate with poor humor and Christmas cheer...

  8. #18
    Join Date
    Feb 2009
    Location
    Durango, CO
    Posts
    3,114
    Quote Originally Posted by iwire View Post
    With 2 AL and a 10 amp load at 240 VAC I come up with less than 5% drop and I doubt the load would be that high. Place a small transformer to get the 120 volts and it's done. Honestly 1700' is not that far, consider the parking lot lighting at your local shopping plaza.
    Good point, and I agree.
    We can think it to death or just get out an do it.
    You have had some time to think. Is there anything else you might want to add?
    If Billy Idol or John Denver is on your Ipod go and re-evaluate your life.

  9. #19
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    4,522
    120606-1133 EDT

    Mr. Spinosa:

    It is really important to know what the actual present load, and future possible loads are expected at the gate. There is possibly a big difference between peak power needed and average power over a day.

    I could possibly supply a 50% continuous load at that distance (120 * 20 = 2400 W) with a 240 V source at the input end and #14 copper wire assuming a 50% duty cycle. The voltage drop would be about 100 V at 10 A. Thus, available power at the destination on a continuous basis is 140 * 10 = `1400 W. This is 33.6 KWH per day at the gate. (I run my whole house on 30 to 40 KWH per day.) At a 50% duty cycle and a 2400 W load 28.8 KWH per day are required.

    To accomplish this goal requires some energy storage and an electronic converter at the destination. My point is not so much to suggest that you do this, but to point out a different perspective. You really need to look at what are the real load requirements at the gate.

    Also note that super capacitors may be a better energy storage device than a regular battery.

    .

  10. #20
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    496
    Quote Originally Posted by gar View Post
    120606-1133 EDT

    Mr. Spinosa:

    It is really important to know what the actual present load, and future possible loads are expected at the gate. There is possibly a big difference between peak power needed and average power over a day.

    ......

    Also note that super capacitors may be a better energy storage device than a regular battery.

    .

    I echo the first part. I'd look at a 13.8VDC operator with a local deep cycle battery. You can run one conductor out & have the charger at the house. Put a diode at the battery. Use a ground return.

    "Wait!" you say.... "Voltage Drop..."

    But that implies current.

    Working backwards... End-state; the battery is fully charged and draws no current from the charger. Before then, yes there is drop, but you're putting some coulombs into the battery. Patience, Grasshopper.

    You do need a way to up the charge voltage to make up for the fixed diode drop.

    Now, iffen I were building it, I might use a 48V->13.8v converter, or even just a series regulator at the battery.

    As for capacitor storage.....I've not looked at such in years and yield to gar.