oversized neutral

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree with Dennis, but ask that you note the FPN at 210.4(A).
This, as far as I know, is as close as the Code comes to recognizing the possible need for an oversized neutral on 3 phase 4 wire MWBC with substantial nonlinear loads.
The true need for such should be based on engineering data.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with Dennis, but ask that you note the FPN at 210.4(A).
This, as far as I know, is as close as the Code comes to recognizing the possible need for an oversized neutral on 3 phase 4 wire MWBC with substantial nonlinear loads.
The true need for such should be based on engineering data.

Good point Gus. Nonlinear loads can change things a bit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't think that there is any place in the NEC where an over-sized neutral is required for a MWBC. Although it's mentioned it's really a design issue.
 