Main bonding jumper

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 4 sets of 500 kcmil alumium (AL) service conductors. The service disconnect is to have wire copper (CU) main bonding jumper. Nec 2014 Table 250.102(C)(1) note #2 is confusing regarding different materials and so sizing is confusing. Based on that table would 3/0 AWG copper main bonding jumper be sufficent? If not then based on that table what would be the size?

Sent from my SM-G935U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The MBJ is sized based on 12.5% of the size of the SEC's in this case 2000 kcmil. If you want to use a copper MBJ you would use the equivalent size of an aluminum MBJ.
 