i am connecting a rooftop mounted 50kw satcon inverter to a nearby 400A 480V subpanel with an 80A breaker. the grounding between the subpanel on the roof and the main panel two floors below is #2. the gec for the main panel is #4/0. the largest dc conductor is #3/0. do i really need to run #3/0 all the way downstairs two floors to the AC grounding electrode?
-
Yes, you do, unfortunately.