    Hello everyone,
    I have 15KV primary - 480Y/277V secondary transformer and then I have a fence around it. I only have 22-3/4" of space on each side of the transformer and 3'-0" on the back and 7' on the front. the fence only has one door in front of the transformer.
    Q1: where in the NEC are the requirements for space clearances on the sides and back of a medium voltage transformer? i have heard it is 2 feet on the sides and on the back but haven't been able to find this in the NEC.
    Q2: Are the clearances above ok for egress? (NFPA 101) i have heard this is 36" but haven't been able to find this either.
    Thanks.
    F413
  2. #2
    Join Date
    Apr 2009
    Olathe, Kansas 338 mi SE of Wingedhorses
    Posts
    2,726
    Heck if I know Bump
    Electricity is Color Blind
    Leave the shirt pocket rules in your pocket.
  3. #3
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,855
    Are there any exposed parts on the back of the equipment?
    Does any routine maintance need to be done on the rear of the transfromer while it is energized?
    Is the primary under the control of a utility?
    Just because you can, doesn't mean you should.
  4. #4
    Join Date
    Dec 2010
    Posts
    1,505
    It would help more to know who owns the transformer. Where is the point of delivery?
  5. #5
    Join Date
    May 2012
    Boca Raton, Fl, USA
    Posts
    1,037
    Patrox... A large HPI company I worked for required:
    a) An 8-foot high fence.
    b) 48-inch minimum distance between the fence and HV terminal side.
    c) 36-inch minimum distance between the fence and the other 3 sides; and
    d) At least two access gates on opposite sides of the fence!
    Regards, Phil
  6. #6
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,457
    I guess it depends on the type of design. I have a dry type 500kVA 480V-4.16kV transformer in a SWGR room next to everything leaving the required working distance per Chapter 1 in the NEC.
    Ron
  7. #7
    Join Date
    Dec 2008
    Towson, MD
    Posts
    40
    Quote Originally Posted by jim dungar View Post
    Jim, the responses to your questions are 1) no, 2)no, 3) this is for a university campus, so it will be a campus feeder connecting to the transformer primary.
    i was just wondering where in the NEC the clearance requirements for an oil filled transformer were and if there were any NFPA requirements for egress from an electrical equipment courtyards. if anyone knows the answers please reply.
    thanks.