Extra Duty Outlet Hoods

Status
Not open for further replies.

cpal

Senior Member
Location
MA
This is out of the 2011 Nec 406.9 (b) Informational Note

Informational Note No. 1: Requirements for extra-duty
outlet box hoods are found in ANSI/UL 514D-2000,​
Cover

Plates for Flush-Mounted Wiring Devices
.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The UL rep at a FEB code class says the standard was not yet complete at that time and a search of the UL code correlation database does not show any listed products. The last edition of UL 514D listed on the UL catalog of standards is April of 2000.
 