Does 70E require arc flash boundries marked on the floor. That is are the boundries marked with something like yellow(caution) paint. Before any work begins are the boundries are physically visible.
Does 70E require arc flash boundries marked on the floor. That is are the boundries marked with something like yellow(caution) paint. Before any work begins are the boundries are physically visible.
The arc flash boundary alerting requirement is met by it being displayed on the AF label.
It's a good idea, IMO, to use additional techniques to identify the boundary, but along with that then there would need to be sitewide training so everyone could know what's being done (i.e. red/yellow/orange paint for AFB)
John M
There is no need to mark the floor, just as there is no need to permanently mark working clearances. The AF boundary only exists when someone is "interacting in a manner that would cause an arc" not just simple interaction.
Many Electrical Safe Work Practices programs require the use of 'caution tape' or other portable/temporary barricades.
Just because you can, doesn't mean you should.
what if electrical panels are in an employee break room. how much room has to be between the panels and a lunch table ?
NFPA70E is fraught with what needs to be done but, purposely, there is not much detail on how to accomplish it.
See the NFPA70E definition of Arc Flash Hazard.
Informational Note #1 says normal operation is normally not an issue, Note #2 is the reference for Zog's posting directing you to the task tables.
But then to make things clearer (?), the committee added Note #2 to 130.7(A), which effectively says; in the experience of the [NFPA70E] committee members normal operation of properly maintained enclosed equipment <600V is not likely a hazard.
So there is no single correct answer, but, statistically it is worse to be operating equipment, than it is walking past or simply sitting in the same room with it.
Just because you can, doesn't mean you should.
No. Only the equipment itself must be labeled, and only for when the incindent energy is larger than 1.2 cal/cm sq. (see attached NFPA 130.5(C)