Thread: Labels inside of a panel

  1. #1
    Join Date
    Nov 2003
    Location
    New Jersey
    Posts
    529

    Labels inside of a panel

    Is there a requirement for manufacturers labels. nameplate stuff, etc to be inside a panel? All panels (Siemens) in a home I looked at yesterday had nothing inside (only label was on the inside of the cover door)
    Attached Images Attached Images  
    Tony Shupenko, PE

  2. #2
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    This what the NEC says:

    408.58 Panelboard Marking. Panelboards shall be durably
    marked by the manufacturer with the voltage and the
    current rating and the number of phases for which they are
    designed and with the manufacturer’s name or trademark in
    such a manner so as to be visible after installation, without
    disturbing the interior parts or wiring.

    There are other requirements for stuff also: High leg identification, fault current, etc....
    "Electricity is really just organized lightning." George Carlin


    Derék

  3. #3
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    18,963
    The enclosure or cabinet is not the panelboard. The cabinet may be used with many different panelboards. The required makings will be on the panelboard (guts) covers.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  4. #4
    Join Date
    Nov 2003
    Location
    New Jersey
    Posts
    529
    Quote Originally Posted by jumper View Post
    This what the NEC says:

    408.58 Panelboard Marking. Panelboards shall be durably
    marked by the manufacturer with the voltage and the
    current rating and the number of phases for which they are
    designed and with the manufacturer’s name or trademark in
    such a manner so as to be visible after installation, without
    disturbing the interior parts or wiring.

    There are other requirements for stuff also: High leg identification, fault current, etc....
    Does the stuff on the panel cover mean anything in this case? Also, any idea why internal information is missing?
    Tony Shupenko, PE

  5. #5
    Join Date
    May 2003
    Posts
    654
    Doubt it as Siemens, and when those panels were branded as Gould / ITE the info has been on the door, mid to late 1970's ITE had them in the panel making them a bear to read when they were so packed full that you had to pry conductors out to read em, the old "10 pounds of manure in a 5 pound bag", CH "Classic" panels I think were one of the last to still place data inside & that ended after the CH & BR panels started sharing the same box & doors, minus some color/ dead front differences.

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    18,064
    I guess if the cabinet and interior is the only one the cover fits then it is probably acceptable.

    Often times they make one box and or cover that is for more than one interior panelboard. If that is the case the label will have to include information for all the possibilities, and can be confusing to identify which unit you have.

  7. #7
    Join Date
    Feb 2003
    Location
    Wisconsin
    Posts
    8,709
    Most product labeling falls under the Listing requirements. If UL doesn't require it, I am pretty sure it won't happen.
    The NEC is concerned with the item 'as installed', so as long as the info eventally is on the finished product, I think artivcle 408 is covered.
    Just because you can, doesn't mean you should.

  8. #8
    Join Date
    Nov 2003
    Location
    New Jersey
    Posts
    529
    Quote Originally Posted by kwired View Post
    I guess if the cabinet and interior is the only one the cover fits then it is probably acceptable.

    Often times they make one box and or cover that is for more than one interior panelboard. If that is the case the label will have to include information for all the possibilities, and can be confusing to identify which unit you have.
    There were stampings inside the "cabinets" (I think I now have the proper term) - at the tops. Was the only marking inside. The cover door sticker "label" appeared to match. Though after reading other posts, there could be other cover that fit. Does this apply to Siemens products (these cabinets were relatively new - within last 10 years or so)?
    Tony Shupenko, PE

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    18,064
    Quote Originally Posted by tonype View Post
    There were stampings inside the "cabinets" (I think I now have the proper term) - at the tops. Was the only marking inside. The cover door sticker "label" appeared to match. Though after reading other posts, there could be other cover that fit. Does this apply to Siemens products (these cabinets were relatively new - within last 10 years or so)?
    I cannot answer that as I am not all that familiar with Siemens products, and seldom install them. When I do encounter them it is usually where they are a part of an existing installation. I can tell you a lot about Square D as that is what I mostly install.

  10. #10
    Join Date
    Nov 2003
    Location
    New Jersey
    Posts
    529
    I have seen many Siemens - 1st time I can remember not seeing any information labels inside.