Originally Posted by
iwire
A new gray area.
Most of us accept if we bring a listed generator to a property and connect it permenantly to electrical equipment in a building the NEC would apply so why don't you think it applies here?
So how would you make the install comply? What would you use for OCPD and disconnect? The inspector didn't want the rigid ran into the solar panel, just close to it, then add a bushing on the end and seal it. The rigid would then run inside to a disconnect with OCP.
Then from the disconnect to the fan using MC cable. If you use MC you would have to cut the wire, thus voiding the mfg. listing (if there is one).
I also can't find in the NEC where it states "rigid" must be used. All I see is "metal raceway."
I personally don't think the inspector knows anymore than I do about PV systems, which in my case is little to none.
That is why I said to ditch the fan!
If you aim at nothing, you will hit it every time!