Have you ever used another circuit breaker in the Panel with a different manufacturer?
However Siemens does not carry a GEFP or even a GFP breaker. Do you think a Eaton or Square D will fit in the panel will this void the UL approval?
Have you ever used another circuit breaker in the Panel with a different manufacturer?
However Siemens does not carry a GEFP or even a GFP breaker. Do you think a Eaton or Square D will fit in the panel will this void the UL approval?
Last edited by Lady Engineer; 06-20-12 at 02:28 PM.
Lady Engineer, P.E. (From NJ)
I reviewed you post a couple of times and I didn't see any specifics but from the subject matter I would assume that you are refering to a 120/240 1ph3w load center with plug on breakers.
These are the C-H classified breakers. please note that that if listed by UL, C-H classified breakers can be used in other manufacturer's panels. The OEM may object to it but it's on l because they don't want other manufacturers breakers used in their panels even tough those breakers have been UL listed as classified breakers.
If the breaker(s) that you propose to use are not included on this chart you may be SOL.
You may have to consider a sub panel from a manufacturer that has suitable breakers available.
That's the neat part of our job, it is the process of solving problems. If it was easy to do it would require anybody sprecial.
GEFP?
Must be a new one on me...
16 GEFP Acronym Definitions
By Rank / Alphabetical
Georgia Education Finance Program
Glinodo Earth Force Programme
Glitter Egg Fluorescentffentliche Petition
Global Endowments, Foundations & Pension
Global Environment Facility Project
Golden Eagle FlightPrep Provides
Good Eats Fan Page
Gouvernance des Entreprises Familiales et Patrimoniales
Government Efficiency & Financial Planning
Government Efficiency and Financial Planning
Graduate Equity Fellowship Program
Green Engineering Flood Plain
Groupement des Enterprises Franches et Partenaires
Groupement des Entreprises Franches & Partenaires
Groupement des Entreprises Franches et Partenaires
Grupo Español de Farmacia Pediátrica
Are you looking for ground fault breaker for a Siemens panelboard? Of course they make them. You must be searching using a term that they don't use.
But to answer your question, generally breaker manufacturers don't bother to go to the expense of listing their breakers to work in competitor's panels. The exception to that is residential commonplace breakers, just because the market is so large for them. but if it's anything remotely specialized that they can't sell a million of, they are not interested.
__________________________________________________ ____________________________
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
I think it was UL that brought it up that a AFCI with a 30ma GFP is allowed to protect heat tracing cable and if I remember right most ITE AFCI's have a 30 ma GFP, one of the major electrical mags published this UL view.
Wayne A. From: N.W.Indiana
Be Fair, Be Safe
Just don't be fairly safe
I think she ment GFEP "ground fault equipment protection" or class B which is no longer used so most just call them GFP or GFEP 30ma or 50 ma, instead of the 5ma for class A I don't think GFPs have been manufactured for a few years now, and its been common to use an AFCI in place as long as it has the GFP (30ma) in it.
Wayne A. From: N.W.Indiana
Be Fair, Be Safe
Just don't be fairly safe
No, you are correct, it's a GFEP breaker sorry for the typo. The code requires GFEP for heat tracing. I designed the wiring for a cooling tower, and per NEC 427.22. The contract installed a GFCI breaker, and I want him to take it out, but Siemens does not make a 120V/ 20A 1P GFEP breaker like C-H and Square D.
Lady Engineer, P.E. (From NJ)
Square D still has QO "EPD" breakers in current catalog. they are 30mA GFCI's and they even have "EPE" model in 3 pole units that are 100mA devices. http://mydigimag.rrd.com/publication/?i=84624
Last time I was interested in just a single pole "EPD" unit it was a lot less cost to use the protective device offered by same manufacturer as the heat trace equipment.