Looks like a good solution. :)
I've used similar 30 amp versions. What size condcutors are you using?
 

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
2 space loadcenter with breaker and flush cover are an option and may cost less.

Hadn't considered that, a good idea, thanks. Around here they call that a "panel-ette" : )

Rob, was going to run 2 #8's with a #10 ground.

Run is 70 ft.

Finished conduit today, lots of saddles and offsets/kicks to get there but fishtape is sitting in pipe waiting !
 
Last edited:

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Hadn't considered that, a good idea, thanks. Around here they call that a "panel-ette" : )

Rob, was going to run 2 #8's with a #10 ground.

Run is 70 ft.

Finished conduit today, lots of saddles and offsets/kicks to get there but fishtape is sitting in pipe waiting !

That switch says non grounding in the link you provided.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I am not saying that, all I am saying is I don't think the specific requirements of 404.9(B) apply here.

It seems that the only way to actually ground this device (call it a controller or a snap switch) is by the mounting screws.
 

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
what about a breaker lock?

I don't think a breaker lock would fly around here. It's
a line of site disco they ask for. The NYC amendments to the NEC contain
a bit of voodoo :cool: Interesting about the grounding aspect of "controller" however,
--we ran a green #8 also, and will bond that to boxes along the way, but, yes, the yoke screws are the grounding for 40A switch.
 

Cavie

Senior Member
Location
SW Florida
Installing 40A 208V tankless HW heater for commercial bathroom.
Architect wants disconnect switch to be flush with wall. There's not
really a good place to put access door for disco in wall.

Thinking of using this:
http://www.leviton.com/OA_HTML/ibeCCtpItmDspRte.jsp?item=267732&section=10042&minisite=10026

Looks as if it would mount in 5 in. box with 1G mud ring.

Has anyone used one of these before ?

Thanks !


Getting #8's folded into a box with that switch will be a chore.
 