If you have a 200 amp meter/main outside and a 200 MLO panel inside, can you tap the load side of the 200 amp breaker, outside in the meter main enclosure? I have been reading online and it appears to be a grey area.
1. It's not really a supply side connection. NEC 705.12(A)
2. If you put another main breaker in the MLO panel would that make it compliant. (assuming it is not compliant as is.)
3. As is is there a possible over current issue?