    M.H. Illusrated Guide to Electrical Exam Prep...2011

    On page 79, for illustrative purposes, Mike's image and calculation of energy used and a monthly cost in a ground fault condition raises a question for me; Why hasn't the fault cleared?

    The example shows a 120V source, 25 ohms to earth ground fault.

    The first thought that comes to my mind is a faulty circuit breaker. The other is an open EGC or an open neutral. Would like to query other possible causes for this condition.
    Charley

  2. #2
    Join Date
    Dec 2010
    Location
    -
    Posts
    1,505
    Quote Originally Posted by ZCBee View Post
    On page 79, for illustrative purposes, Mike's image and calculation of energy used and a monthly cost in a ground fault condition raises a question for me; Why hasn't the fault cleared?

    The example shows a 120V source, 25 ohms to earth ground fault.

    The first thought that comes to my mind is a faulty circuit breaker. The other is an open EGC or an open neutral. Would like to query other possible causes for this condition.
    Can't see the picture, but according to your numbers, the current is only 4.8 amps. a breaker will hold that for a very long time.

  3. #3
    Join Date
    Feb 2009
    Location
    Reno, NV
    Posts
    50
    Yes, I was thinking of a GFCI protected circuit. I agree, it would pass the 4.8A.
    Charley

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,114
    Even at 6 ohms a 20 amp circuit @ 120V will only have 20 amps on it. It would stay like that for some time.