Thread: Question on using aluminum conductor romex for a sub panel feeder in a residence???

  1. #1
    Join Date
    Feb 2007
    Posts
    127

    Question on using aluminum conductor romex for a sub panel feeder in a residence???

    My electrician suggested using an aluminum conductor romex to feed a sub panel in a standard residence (240V single phase). The sub panel will be a 200A rated panel and the breaker for the romex is a 200A circuit breaker. The distance is approx. 110' long. Is there a romex with aluminum conductors available in an adequate size/gauge for this application??? Any input would be greatly appreciated. Thanks

  2. #2
    Join Date
    Aug 2008
    Location
    NH
    Posts
    1,274
    deleted post
    "Appliances and wiring will burn out to protect fuses"

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,279
    You need to use another wiring method. Either MC cable or SE cable would work.

    III. Construction Specifications

    334.104 Conductors. The 600-volt insulated conductors
    shall be sizes 14 AWG through 2 AWG copper conductors
    or sizes 12 AWG through 2 AWG aluminum or copper-clad
    aluminum conductors. The communications conductors
    shall comply with Part V of Article 800
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  4. #4
    Join Date
    Feb 2007
    Posts
    127
    I just did a little research. It looks like the following will be acceptable:

    AL 4/0 SER 200 A Aluminum 4/0-4/0-4/0-2/0 Service feeder wire for 200A breaker panel

    Any input on this?

  5. #5
    Join Date
    Oct 2006
    Location
    Litchfield, CT
    Posts
    8,622
    Quote Originally Posted by jango View Post
    I just did a little research. It looks like the following will be acceptable:

    AL 4/0 SER 200 A Aluminum 4/0-4/0-4/0-2/0 Service feeder wire for 200A breaker panel

    Any input on this?
    Yeah, 4/0 AL is not big enough for a sub panel at 200 amps.
    "Electricity is actually made up of extremely tiny particles called electrons, that you cannot see with the naked eye unless you have been drinking."

  6. #6
    Join Date
    Feb 2007
    Location
    USA
    Posts
    3,885
    Yea may not work depending on the code version you are working under.
    Used to do it but not now, in my area unless you use a lower breaker say 175amps.
    Many don't even realize.
    You can use a lower breaker to comply.

  7. #7
    Join Date
    Feb 2003
    Location
    San Francisco Southbay
    Posts
    1,870
    Based on 2008 and assuming the subpanel will supply ALL of the loads, 310.15(b)(6) allows a 4/0 aluminum for a 200Amp feeder.

    Am i missing something?
    Edward
    Education is a progressive discovery of our ignorance.

  8. #8
    Join Date
    Sep 2011
    Location
    woodbridge, ct. USA
    Posts
    378
    You might be missing something. Is it a sub-panel or the main panel but located away from the meter? I believe for a sub-panel it's 310.16 and 4/0 Alum is 180a at 75 degrees. This came up a while ago with using #2 SER for a 100a sub-panel. It is only rated 90a.

  9. #9
    Join Date
    Feb 2007
    Location
    USA
    Posts
    3,885
    When can you use the next higher breaker. I don't think they make a 180?

  10. #10
    Join Date
    Feb 2003
    Location
    Mike P. Columbus Ohio
    Posts
    3,568
    Quote Originally Posted by edward View Post
    Based on 2008 and assuming the subpanel will supply ALL of the loads, 310.15(b)(6) allows a 4/0 aluminum for a 200Amp feeder.

    Am i missing something?
    Are you saying that you have a disco (only) ahead of this panel?
    Inspector Mike