Transfer Switch Install - Feeders Pass Thru Meter?

Status
Not open for further replies.
Was checking out a job, Meter has a nipple on back that feeds thru to panel. Was wondering if I could put 2 nipples off of meter to transfer switch (one for service conductors and one for feeder conductors) and pass thru meter to panel. 230.7 was only thing I saw that says can't mix in raceway which they would be installed in seperate raceways just would be in same enclosure
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Was checking out a job, Meter has a nipple on back that feeds thru to panel. Was wondering if I could put 2 nipples off of meter to transfer switch (one for service conductors and one for feeder conductors) and pass thru meter to panel. 230.7 was only thing I saw that says can't mix in raceway which they would be installed in seperate raceways just would be in same enclosure

NEC might not care but I'd say the POCO does. You need to check with them.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
'Raceway' is a bit vaguely defined. I've seen inspectors refer to enclosures as raceways. I'd see it as a gamble unless you get it pre-approved or know the inspector well.
 