408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
NATIONAL ELECTRICAL CODE 2011 Edition
408.41.
That code reference is for neutrals, not for grounds.
I believe that some older panels were rated to have two equally-sized ground wires under one screw terminal, though I do not have a code reference, or if it has changed throughout the years.
Oops you're correct I thought it said grounded. :ashamed1:
That's a slight exaggeration.. . . I am a full four code cycles behind most of the rest of the country.
Here's a related question: If one connects three neutrals (3ph) from adjacent circuits together within the panel because there aren't enough neutral terminals, must the breaker handles still be tied?408.41.
Here's a related question: If one connects three neutrals (3ph) from adjacent circuits together within the panel because there aren't enough neutral terminals, must the breaker handles still be tied?
(<>)
250.8 Connection of Grounding and Bonding Equipment. (A) Permitted Methods. Equipment grounding conductors, grounding electrode conductors, and bonding jumpers shall be connected by one or more of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
110.14(A)Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors. Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
110.3(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
In that case, I'm a bad puddy tat.By definition you have created MWBC so yes.
And I was picturing two bare wires wrapped around a screw in a box or on a device, not wires going into a ground bar in a panel.
Here's a related question: If one connects three neutrals (3ph) from adjacent circuits together within the panel because there aren't enough neutral terminals, must the breaker handles still be tied?
This has nothing to do with switching. It's a case where three simple single-phase circuits are added to an existing three-phase panel, but there are not three neutral terminals available, so I joined the three neutrals to a single pigtail to land in one neutral terminal in the panel. Several neutrals are already doubled up.Hmmm... my head says heck ya... but need to find the code now...
But.. in the case the person is calling for... where the owner wants the three circuits run so he can flip a switch and cut all three off at once, wouldn't that be a great spot for a relay or a sub panel? Run a four breaker sub panel that can be cut off easily by the door, and the three circuits in it... one cable from it back to main panel... its main breaker or switch cuts power to all three breakers. Or is there a safety reason why he wants all three to cut off if any of them cut off? More needs to be known.
My initial thought when I read OP, then after seeing first couple replies I was going to ask what it the application?And I was picturing two bare wires wrapped around a screw in a box or on a device, not wires going into a ground bar in a panel.