    Does a large health club need a full fire alarm if it is sprinklered?

    I know that many types of buildings do not need a full fire alarm system if they are sprinklered (like small offices, retail, etc). But other types (like churches, hospitals, etc) need full fire alarm systems even if they are sprinklered. What about a 20,000 health club?
    "God help us, we're in the hands of engineers!"
    --Malcolm as he climbs into the Jurassic Park remote-contolled jeep.

  2. #2
    Join Date
    Jan 2009
    Location
    Massachusetts, New Hampshire border
    Posts
    1,617
    Quote Originally Posted by donw View Post
    I know that many types of buildings do not need a full fire alarm system if they are sprinklered (like small offices, retail, etc). But other types (like churches, hospitals, etc) need full fire alarm systems even if they are sprinklered. What about a 20,000 health club?


    20000 what? Square foot? Rated occupancy? Number of treadmills?


    What building code governs?
    What occupancy classification is it?
    What does local codes show?
    What does the FD say? (most important place to check most likely. Ask hypothetical questions, you don't have to mention the actual location)

    You will probably have to install notification throughout if it's a place of assembly. RTU's over 2000 CFM probably need duct smokes. Spot smokes in a few other locations....but check all the above first

  3. #3
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,012
    Quote Originally Posted by nhfire77 View Post
    20000 what? Square foot? Rated occupancy? Number of treadmills?


  4. #4
    Join Date
    Jun 2006
    Location
    Arizona
    Posts
    173
    Quote Originally Posted by nhfire77 View Post
    20000 what? Square foot? Rated occupancy? Number of treadmills?


    What building code governs? IBC
    What occupancy classification is it? Good question
    What does local codes show? I don't think any local code addresses this. It's probably the IBC or NFPA 72.
    What does the FD say? (most important place to check most likely. Ask hypothetical questions, you don't have to mention the actual location) Thanks, good idea

    You will probably have to install notification throughout if it's a place of assembly. RTU's over 2000 CFM probably need duct smokes. Spot smokes in a few other locations....but check all the above first
    I wonder if a health club is a place of assembly
    "God help us, we're in the hands of engineers!"
    --Malcolm as he climbs into the Jurassic Park remote-contolled jeep.

  5. #5
    Join Date
    Jan 2009
    Location
    Massachusetts, New Hampshire border
    Posts
    1,617
    Technically an engineer is supposed to make the classification, but. I know better:

    2012 IBC
    303.4 Assembly Group A-3.
    Assembly uses intended for worship, recreation or amusement and other assembly uses not classified elsewhere in Group A including, but not limited to:

    Amusement arcades
    Art galleries
    Bowling alleys
    Community halls
    Courtrooms
    Dance halls (not including food or drink consumption)
    Exhibition halls
    Funeral parlors
    Gymnasiums (without spectator seating)
    Indoor swimming pools (without spectator seating)
    Indoor tennis courts (without spectator seating)
    Lecture halls
    Libraries
    Museums
    Places of religious worship
    Pool and billiard parlors
    Waiting areas in transportation

  6. #6
    Join Date
    Jun 2006
    Location
    Arizona
    Posts
    173
    Thanks, nhfire77. Great answer.
    "God help us, we're in the hands of engineers!"
    --Malcolm as he climbs into the Jurassic Park remote-contolled jeep.

  7. #7
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    502
    Quote Originally Posted by donw View Post
    I wonder if a health club is a place of assembly

    We are gathered here today to worship our bodies & more so, our egos....

  8. #8
    Join Date
    Jan 2007
    Location
    New Jersey
    Posts
    846
    If your using the IBC 2012 it would just need horn ans strobes uless the occupancy was over a thousand then they would need voice/alarm communication.

    [F] 907.2.1 Group A.
    A manual fire alarm system that activates the occupant notification system in accordance with Section 907.5 shall be installed in Group A occupancies where the occupant load due to the assembly occupancy is 300 or more. Group A occupancies not separated from one another in accordance with Section 707.3.9 shall be considered as a single occupancy for the purposes of applying this section. Portions of Group E occupancies occupied for assembly purposes shall be provided with a fire alarm system as required for the Group E occupancy.

    Exception:
    Manual fire alarm boxes are not required where the building is equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1 and the occupant notification appliances will activate throughout the notification zones upon sprinkler waterflow.
    Rick Napier
    Inspector and Instructor