Closed Thread
Results 1 to 4 of 4
Thread: Box fill question and DC motor question.
  1. #1
    Join Date
    May 2012
    Miami
    Posts
    38
    Hi there!, please I need to solve this two questions, I having trouble with them, looks very simple but there is something I cannot find right. Thank you !!!!!
    1. What size of box is required for two #6 conductors, one #10 ground that leave the box, one #12 ground and two #12 conductors, the #6 conductors has internal clamps and the #12 has external clamps.
    2. what is the efficiency of one 5HP/230 DC motor ?
  2. #2
    Join Date
    Jul 2012
    Simpsonville, South Carolina
    Posts
    1
    Box Fill Calculation
    I gave your question about box fill a shot; Let me know what you think.
    TABLE 314.16(B) ALL OF ARTICLE 314.16
    2- #6 conductors = 10 cu in
    1- #10 ground = 2.5 cu in
    2- #12 conductors = 4.5 cu in
    1 internal clamp (#6) = 5.0 cu in
    Total: 22 cubic in = 4 x 2 1/8 square box
    for your motor question, I don't think there is enough info. Efficiency = output of true power/ input of true power
    the true output of a DC 5HP, 230v motor is: 1hp = 746watts; 5 * 746 = 3,730watts
    Let me know if this helps.
  3. #3
    Join Date
    Jul 2012
    Arizona
    Posts
    1
    Dc motor effciencies
    I have an old American Electician Hand book and it gives some approximate Eff: 5HP at half load 77% Full load 81.5 % hope this helps some
  4. #4
    Join Date
    Sep 2008
    UK
    Posts
    4,739
    Quote Originally Posted by AZBob View Post
    I'm pretty ancient and I've dealt with quite a lot of DC drives. Not very often as small as 5HP but those figures seem like a reasonable basis for calculations.
Closed Thread
Tags for this Thread
Posting Permissions
  • You may not post new threads