As an example take a 55kW 400V 3-phase motor.
Driven directly from the supply it will take about 107A FLC
Use an active front end and that will take about 89A.
Both 55kW rating.
The supply loading for one is 74 kVA, the other 62 kVA.
The supply power is 59kW for one and 62kW for the other.
Would you perhaps like to reconsider your comment that installed KVA, KW and current are all equivalent?
You mentioned about two motors: one with active front end while the other one without it. If the one with the active front one is so provided in the field, such modification in its rating need be clearly displayed.