Does anyone know the required fusing formula for cutouts, to protect a pole mounted cap bank ? Does it follow IEEE or is there another code body?
Would I have to acount for Inrush current and oversize for about 50% ish or is there a law of the land?
Does anyone know the required fusing formula for cutouts, to protect a pole mounted cap bank ? Does it follow IEEE or is there another code body?
Would I have to acount for Inrush current and oversize for about 50% ish or is there a law of the land?
Last edited by aelectricalman; 07-18-12 at 01:59 PM. Reason: IEEE not IIIE
Chris Hill, EE,ME,GA-CR
Power Factor Correction
Ops Engineering
For a grounded wye bank:
Fuse link 100% rating = 1.35 * kvar_3ph / sqrt(3) / kV_LL
For a 150% rated fuse like a NEMA T-link, divide the current value above by 1.5
add:
For an ungrounded wye bank:
Fuse link 100% rating = 1.25 * kvar_3ph / sqrt(3) / kV_LL
The 25-35% adder comes from the normal allowance of:
10% for voltage
5%-15% for capacitor tolerance
5% for harmonics on ungrounded or 10% for harmonics on grounded wye
Last edited by mivey; 07-18-12 at 04:53 PM.