Thread: Why is breaker tripping?

  1. #11
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    2,876
    I'll put it this way:

    The chances that it is something on the LINE side causing ONLY THIS BREAKER to trip are far far slimmer than something on the LOAD side. If you had for example a grid glitch that caused a brief outage and if it came back on almost immediately, and if you had some big spinning loads, then if their motors had not had time to collapse the magnetic fields, the regen from those big spinning loads that can occur because the restoration of power is at a different frequency than the regen can cause a severe transient that can trip the magnetic trips of the breaker. Notice there are a lot of "ifs" in there and by the way, you could STILL consider this a load problem, because all you have to do to fix it is to not allow loads to stay on after an outage.

    Or how about this: the likelihood that the breaker is DOING ITS JOB and preventing a fire because of some yet undiscovered but perfectly plausible issue on the load side are far greater than it being defective or getting fooled by some "phantom" even on the line side.

    Before wasting a lot more time, I'd find out if a coordination study was ever done. If it was, then immediately check ALL other protective devices down stream of this breaker to make sure they are EXACTLY as depicted in that study. The one that is not the same or the one that is new and not included is the first place to look for undiscovered problems. If there was NO coordination study done (as I suspect), then that may be problem #1. You may have a down stream protective device that is set to trip at a level higher than the setting of this breaker. That's exactly what a "coordination" study prevents, it's intended to make sure that protective device settings are coordinated so that faults are cleared at the lowest (closest) possible level.
    __________________________________________________ ____________________________
    "Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
    — Kilgore Trout (via Kurt Vonnegut)

  2. #12
    Join Date
    Oct 2004
    Location
    Antipolo City
    Posts
    455
    Quote Originally Posted by Jraef View Post
    I'll put it this way:

    The chances that it is something on the LINE side causing ONLY THIS BREAKER to trip are far far slimmer than something on the LOAD side. If you had for example a grid glitch that caused a brief outage and if it came back on almost immediately, and if you had some big spinning loads, then if their motors had not had time to collapse the magnetic fields, the regen from those big spinning loads that can occur because the restoration of power is at a different frequency than the regen can cause a severe transient that can trip the magnetic trips of the breaker. Notice there are a lot of "ifs" in there and by the way, you could STILL consider this a load problem, because all you have to do to fix it is to not allow loads to stay on after an outage.

    Or how about this: the likelihood that the breaker is DOING ITS JOB and preventing a fire because of some yet undiscovered but perfectly plausible issue on the load side are far greater than it being defective or getting fooled by some "phantom" even on the line side.

    Before wasting a lot more time, I'd find out if a coordination study was ever done. If it was, then immediately check ALL other protective devices down stream of this breaker to make sure they are EXACTLY as depicted in that study. The one that is not the same or the one that is new and not included is the first place to look for undiscovered problems. If there was NO coordination study done (as I suspect), then that may be problem #1. You may have a down stream protective device that is set to trip at a level higher than the setting of this breaker. That's exactly what a "coordination" study prevents, it's intended to make sure that protective device settings are coordinated so that faults are cleared at the lowest (closest) possible level.
    Agree 100%, especially

    The chances that it is something on the LINE side causing ONLY THIS BREAKER to trip are far far slimmer than something on the LOAD side.
    NEC 1968 and 1948

  3. #13
    T.M.Haja Sahib Guest
    One last point. In case UV relay is provided in the breaker, check whether it has any time delay arrangement also. The breaker may be tripping due to wrong setting of the time delay of UV relay.

  4. #14
    Join Date
    Aug 2004
    Location
    Plainfield, IN
    Posts
    890
    As others have said, a load side cause or faulty breaker is much more probable than a line side cause. One possible line side cause is capacitor switching transient if the breaker is tripping on ground fault and the GFI is monitoring the neutral to ground bond. See this link for more information.

  5. #15
    Join Date
    Jul 2004
    Location
    Texas by the Gulf, geat crab, great shrimp
    Posts
    5,106
    Quote Originally Posted by robbietan View Post
    Agree 100%, especially

    The chances that it is something on the LINE side causing ONLY THIS BREAKER to trip are far far slimmer than something on the LOAD side.
    Then there is the potential of having a fault(y/ing) breaker.
    Laszlo Z Weress
    Staff Engineer

    Business is competition, and the ultimate competition is war. All is fair in love and war.

  6. #16
    Join Date
    Oct 2004
    Location
    Antipolo City
    Posts
    455
    Quote Originally Posted by weressl View Post
    Then there is the potential of having a fault(y/ing) breaker.
    the utility would consider that as "loadside"...
    NEC 1968 and 1948