Closed Thread
Results 1 to 4 of 4
Thread: sccr
  1. #1
    Join Date
    Aug 2004
    Posts
    9,156
    sccr
    So I need to get 65kA in a panel that has some 20A breakers.
    There are of course, no 20A breakers with a rating that high, even series rated. Unless one adds another breaker in the mix. Its like using a CB as a distribution block. It bugs me, but it is a workable and relatively inexpensive answer to the problem.
    Bob
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    7,960
    Quote Originally Posted by petersonra View Post
    What voltage do you have?
    Square D QO breakers (actually QH) are 65kAIC rated upto 240V.
    Or, simply get a '480V' breaker and use it at 208V. I would bet that every manufacturer has this option for 65kAIC.
    But, based on your other postings I am guessing that you want a 480V 'DIN rail' style breaker for a control circuit.
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    Aug 2004
    Posts
    9,156
    Quote Originally Posted by jim dungar View Post
    Its for some smallish 480V motors with a 1200 A main CB on the control panel.
    Bob
  4. #4
    Join Date
    Feb 2003
    Wisconsin
    Posts
    7,960
    65kAIC is a standard rating for 480V breakers. You should be able to find one pretty easily, but they will be about 4"w by 7"tall
    Look into something like the Square D HJL36020(?)
  5. #5
    Join Date
    Jul 2006
    San Francisco, CA, USA
    Posts
    2,832
    Most of the IEC type "Manual Motor Starters" are rated 65kAIC when used in a "Group Fusing" application such as you are describing.
    __________________________________________________ ____________________________
    "Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
    — Kilgore Trout (via Kurt Vonnegut)
Closed Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts