Is a fused disconnect required if transformer secondary conductors are over 10 feet?

Or a circuit breaker. Unless it is a single phase 2-wire secondary or three phase 3-wire secondary and complies with 240.21(C)(1).

Transformer secondary conductors protection must comply with one of the methods in 240.21(C)(1) through (C)(6).
 

cppoly

Senior Member
Location
New York
Thanks, I should have kept reading the section but there is a section for <25' secondary conductors.

But, does anyone have the 2014 NEC handbook? Transformer section 240.21(C)(2) commentary gives a transformer example and says to apply section 240.21(C)(2) (transformer secondary not over 10’) to determine minimum secondary conductor size. But the example, applies 1/10th rating of the primary OCPD which has nothing to due with the rules of section 240.21(C)(2). Unless I’m reading this wrong, is this commentary not correct??
 