    DC Fed From Another Building

    Is there anything in the code that would prohibit the Inverter/batteries located in one building and the array located on another with the DC feed underground between the two?

  2. #2
    Join Date
    May 2011
    Posts
    1,232
    No, nothing in the code that prohibits this per se, as far as I see it.

    If the buildings are on different properties or service meters the AHJ might have a problem with it (whether it's AC or DC). I would get approval in advance. And grounding could be complicated or problematic if the buildings' current grounding electrode systems are not already connected.

    I would recommend a DC disconnect at the building with the array, regardless of whether the conductors enter the building. Just from the point of view of general safety and AHJ issues that have been discussed here. I don't think it's a code requirement per se.

    I'll assume you're not seeking input on the advantages or disadvantages of making the underground run AC instead of DC.

  3. #3
    Join Date
    Jun 2012
    Location
    Oregon, US
    Posts
    32
    Both buildings are on the same property and fed from same service. We are planning on installing a DC disconnect on the array building.