240.4 (C) States that the ampacity of the conductors it protects shall be equal to or greater than the rating of the overcurrent device. I understand that.
If I have an adjustable trip circuit breaker that is adjusted to the load do I still have to size the conductors to the breaker rating or can I size them to the load?
This would be covered by 240.6 (C).
If I have an adjustable trip circuit breaker that is adjusted to the load do I still have to size the conductors to the breaker rating or can I size them to the load?
This would be covered by 240.6 (C).