Originally Posted by
Timlocke
I am looking at installing a new camera system in a Class 1 Div 2 area.
The ethernet switches will be installed in a Type Z purged cabinet. The other end of the cable will be in an explosion proof camera enclosure.
The conduit will cross several Hazloc boundaries so we are using seal offs at both enclosures.
Is it necessary to split out the ethernet cable in the seal off or can the fact that both ends are inside enclosures be used to prevent that?
Thank you in advance for your opinions.
Tim
Why not route it in a wire channel(basket) as a PLTC cable? There would be a need for a cable gland - Crouse-Hinds CGB, or similar - on the purged end as it only required to maintain, contain the pressurization and minimize airloss. On the other end, if the camera is trully XP rated that requires the potential explosion to be contained within, then a seal fitting should take care of the business. If you are thinking of splitting the power feed and the signal(Ethernet) feed into the camera body, feed the power conduit and the Ethernet cable into a condulet and couple that into the camera body. When installing the seal, just remove the jacket where it is surrounded by the sealing material, from the Ethernet Cable, exposing single conductors/wires.
If the camera is XP rated to be suitable for both Div. 1 and 2, when installing it in Div. 2 area you may not need to install seal(s) if the camera and PTZ does not contain heating or arc producing components within. Confirm it with the manufacturers engineering deaprtment though, in writing.
Laszlo Z Weress
Staff Engineer
Business is competition, and the ultimate competition is war. All is fair in love and war.