    Ethernet Cable in Class 1 Div 2 area

    I am looking at installing a new camera system in a Class 1 Div 2 area.

    The ethernet switches will be installed in a Type Z purged cabinet. The other end of the cable will be in an explosion proof camera enclosure.

    The conduit will cross several Hazloc boundaries so we are using seal offs at both enclosures.

    Is it necessary to split out the ethernet cable in the seal off or can the fact that both ends are inside enclosures be used to prevent that?

    Thank you in advance for your opinions.

    Tim

  2. #2
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    1,037
    Quote Originally Posted by Timlocke View Post
    I am looking at installing a new camera system in a Class 1 Div 2 area.

    The ethernet switches will be installed in a Type Z purged cabinet. The other end of the cable will be in an explosion proof camera enclosure.

    The conduit will cross several Hazloc boundaries so we are using seal offs at both enclosures.

    Is it necessary to split out the ethernet cable in the seal off or can the fact that both ends are inside enclosures be used to prevent that?

    Thank you in advance for your opinions.

    Tim
    If I understand your situation correctly... Apparently the camera and the ethernet switch are in Class 1 Div 2 areas. My first question is why? The situation that you describe implies that it would be easy to place the switch outside a Div 2 boundary. So, that said, the purged cabinet would likely need seals to maintain the airtight integrity, not the same as needing a seal to contain explosize gasses and fire. These are two different things. The Camera only needs a seal if the interior components have the potential to ignite the gasses. It is at each Hozloc boundary that code will require seals. As long as the cable is continuous, it can be treated as any other low voltage wire or cable and I don't understand your terminology of "splitting" it out. It can't be in a conduit with class one or power wiring anyway, and you have to create space between each conductor or cable in a seal, otherwise what do you mean?


    I know what I don't know, and I know where to go to find it!

  3. #3
    Join Date
    Jul 2004
    Location
    Texas by the Gulf, geat crab, great shrimp
    Posts
    5,407
    Quote Originally Posted by Timlocke View Post
    I am looking at installing a new camera system in a Class 1 Div 2 area.

    The ethernet switches will be installed in a Type Z purged cabinet. The other end of the cable will be in an explosion proof camera enclosure.

    The conduit will cross several Hazloc boundaries so we are using seal offs at both enclosures.

    Is it necessary to split out the ethernet cable in the seal off or can the fact that both ends are inside enclosures be used to prevent that?

    Thank you in advance for your opinions.

    Tim
    Why not route it in a wire channel(basket) as a PLTC cable? There would be a need for a cable gland - Crouse-Hinds CGB, or similar - on the purged end as it only required to maintain, contain the pressurization and minimize airloss. On the other end, if the camera is trully XP rated that requires the potential explosion to be contained within, then a seal fitting should take care of the business. If you are thinking of splitting the power feed and the signal(Ethernet) feed into the camera body, feed the power conduit and the Ethernet cable into a condulet and couple that into the camera body. When installing the seal, just remove the jacket where it is surrounded by the sealing material, from the Ethernet Cable, exposing single conductors/wires.

    If the camera is XP rated to be suitable for both Div. 1 and 2, when installing it in Div. 2 area you may not need to install seal(s) if the camera and PTZ does not contain heating or arc producing components within. Confirm it with the manufacturers engineering deaprtment though, in writing.

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,529
    I think that this question is about the provisions of 501.15(D)(1).
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  5. #5
    Join Date
    Jul 2004
    Location
    Texas by the Gulf, geat crab, great shrimp
    Posts
    5,407
    Quote Originally Posted by don_resqcapt19 View Post
    I think that this question is about the provisions of 501.15(D)(1).
    That para is for CLassI, Division 1, his questions were addressing application in Division 2 area, so it would be (E).