Thread: Bonding Conductor in EMT Fitting

  1. #11
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    17,301
    Quote Originally Posted by ron View Post
    In the picture, is the bonding from the conductor in the EMT to the EMT occuring with a #10 or something small like that?
    Not sure I follow, the GEC in that 1.25" RMC is 500 kcmil.
    Rob

    Chief Moderator

  2. #12
    Join Date
    Aug 2006
    Location
    Miami Fla.
    Posts
    6,700
    Quote Originally Posted by infinity View Post
    Not sure I follow, the GEC in that 1.25" RMC is 500 kcmil.
    Those don't look like listed fittings but I can't find anything that states they have to be.

  3. #13
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    17,301
    Quote Originally Posted by chris kennedy View Post
    Those don't look like listed fittings but I can't find anything that states they have to be.
    They certainly are not listed as depicted in the photo but no one manufactures a fitting to terminate a 500 kcmil GEC to a 1.25" raceway so someone improvised.
    Rob

    Chief Moderator

  4. #14
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    23,557
    Quote Originally Posted by ron View Post
    In the picture, is the bonding from the conductor in the EMT to the EMT occuring with a #10 or something small like that?
    No it is a bonding strap which is pary of the lug. I assume if the lug accepts a 4/0 then so does the entire lug.

  5. #15
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    3,001
    Quote Originally Posted by infinity View Post
    Not sure I follow, the GEC in that 1.25" RMC is 500 kcmil.
    I meant the small wire going from the grounding bushing to the tap onto the 500's
    Ron

  6. #16
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    883
    Quote Originally Posted by ron View Post
    I meant the small wire going from the grounding bushing to the tap onto the 500's
    Ron, that is not a wire. It just a side view of a standard copper lug.
    Curt Swartz
    Electrical Contractor

  7. #17
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    17,205
    Quote Originally Posted by infinity View Post
    They certainly are not listed as depicted in the photo but no one manufactures a fitting to terminate a 500 kcmil GEC to a 1.25" raceway so someone improvised.
    OZ does. Look at their GH-125B.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  8. #18
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    17,301
    Quote Originally Posted by don_resqcapt19 View Post
    OZ does. Look at their GH-125B.
    Thanks for the link. Our supply house said that no one makes them.
    Rob

    Chief Moderator