    Fire Alarm Questions

    Can fire alarm cable be run exposed or concealed (not in conduit) in non-sanctuary areas of a church?

    Does anyone thing smoke detectors need to be located under a church sanctuary balcony? The balcony is 13 feet deep and has a flat ceiling below (so smoke will not be trapped against the back wall). There are smoke detectors above.

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    3,906
    Generally they can be exposed or concealed as long as they are not exposed to physical damage. Some AHJ' consider <10' exposed requires protection.

    On high ceilings, sometimes you need to locate detectors at intermediate levels (under a balcony) to catch smoke conditions during a smoke stratification condition.
    Ron

  3. #3
    Join Date
    Jan 2009
    Location
    NH
    Posts
    1,680
    Quote Originally Posted by olc View Post
    Can fire alarm cable be run exposed or concealed (not in conduit) in non-sanctuary areas of a church?

    Does anyone thing smoke detectors need to be located under a church sanctuary balcony? The balcony is 13 feet deep and has a flat ceiling below (so smoke will not be trapped against the back wall). There are smoke detectors above.
    760.53(A). 7' or above can be unprotected.

  4. #4
    Join Date
    Oct 2012
    Location
    Ny, Ny
    Posts
    3
    Are they any exemptions to this rule like in an IDF where it has to be fully ran in conduit? Or the 7 ft rule stands.