    Fire Alarm Questions

    Can fire alarm cable be run exposed or concealed (not in conduit) in non-sanctuary areas of a church?

    Does anyone thing smoke detectors need to be located under a church sanctuary balcony? The balcony is 13 feet deep and has a flat ceiling below (so smoke will not be trapped against the back wall). There are smoke detectors above.

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    3,377
    Generally they can be exposed or concealed as long as they are not exposed to physical damage. Some AHJ' consider <10' exposed requires protection.

    On high ceilings, sometimes you need to locate detectors at intermediate levels (under a balcony) to catch smoke conditions during a smoke stratification condition.
    Ron

  3. #3
    Join Date
    Jan 2009
    Location
    Massachusetts, New Hampshire border
    Posts
    1,626
    Quote Originally Posted by olc View Post
    Can fire alarm cable be run exposed or concealed (not in conduit) in non-sanctuary areas of a church?

    Does anyone thing smoke detectors need to be located under a church sanctuary balcony? The balcony is 13 feet deep and has a flat ceiling below (so smoke will not be trapped against the back wall). There are smoke detectors above.
    760.53(A). 7' or above can be unprotected.

  4. #4
    Join Date
    Oct 2012
    Location
    Ny, Ny
    Posts
    3
    Are they any exemptions to this rule like in an IDF where it has to be fully ran in conduit? Or the 7 ft rule stands.