Apparently your crash course did not include defining all the necessary variables in such a design. Are you sure this is not homework?
Some of the missing information:
The lowest temperature at the installation site figures into the calculation of the number of series PV modules that are allowable. High temperature figures into wire sizing.
Also needed is the voltage limits of the inverter if you have picked one. If the inverter is not specified, then many need to be considered. The AC breaker depends on the specifications of the inverter for the service voltage. Wire size depends on the circuit breaker and temperature.
Distances: wire length figures into some of the calculations, especially the AC cable.
You do not specify the voltage of the 3-phase service.
Location: electrical codes vary.
In general, if there are four or more parallel PV strings to an inverter, consider the use of a DC combiner. Conduit fill derating is a factor when there are more wires in a conduit.
Smaller inverters are usually single phase. If you need to use multiple smaller inverters, use three the same size.
Most inverter manufacturers have websites with utilities for some of these calculations.
There is likely no single optimum design, but there are many proper designs. A full design must also cover many utility issues, grounding, labeling, consideration of the capability of the point of connection and its ratings, how to mount the PV modules, etc.