    Power for motor

    I like to ask you guys for a way to solve a problem before it happens. We have a 3/4 hp motor 120 volt that needs to be running at all times. Should we lose power just from the feeding cb that feeds the building this motor is in could cause a major problem for the company. There is a generator on the switchgear but that only would come on if power is lost to all the switchgear.
    What is the best way to protect critical equipment when only parcal power is lost? There are about 12 main switchgear breakers.
    It could be atleast 1 hour before someone can get to this 3/4 hp motor to make a fix should it lose power. Would a ups work ?

  2. #2
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    3,983
    120803-2343 EDT

    An appropriate UPS with a sufficiently large battery could be used. This would not be a small computer UPS. Appropriate means it could properly drive the motor without hurting the UPS or motor.

    A brushless DC motor (really a synchronous AC motor) with its drive, or a VFD of some sort designed for your motor, and a large battery added to the the DC bus of the drive might work.

    For 1 HP assume 1 kWh of energy to provide your 1 hour requirement. An ordinary large auto battery has about 12 * 50 = 0.6 kWh of storage. Maybe somewhat less.

    There are other details I am not getting into, and the above values are very much ballpark estimates.

    .

  3. #3
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    17,201
    If the motor is that critical, it needs its own transfer switch so that when the motor circuit fails, the generator will start. What about other modes of failure? Loss of power is not the only thing that will stop the motor from running.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  4. #4
    Join Date
    Nov 2007
    Posts
    254
    Quote Originally Posted by don_resqcapt19 View Post
    If the motor is that critical, it needs its own transfer switch so that when the motor circuit fails, the generator will start. What about other modes of failure? Loss of power is not the only thing that will stop the motor from running.
    Yeah, I think you need to have a backup identical unit that can be switched-in if the online equipment fails. We call that "redundancy".

  5. #5
    Join Date
    Jul 2011
    Location
    stanton
    Posts
    87
    Great information. Will look into my options now. thanks to all .

  6. #6
    Join Date
    Jul 2009
    Location
    Ware Shoals, South Carolina
    Posts
    976
    Besides, or in addition to the generator the transfer switch could use a source from the other switchgear bus that is still energized. You would have three sources & the generator start could stay as it is.
    Advise is a dangerous gift, even from the wise to the wise.

  7. #7
    Join Date
    Jul 2012
    Location
    knoxville tn
    Posts
    46
    Quote Originally Posted by hawkeye23 View Post
    I like to ask you guys for a way to solve a problem before it happens. We have a 3/4 hp motor 120 volt that needs to be running at all times. Should we lose power just from the feeding cb that feeds the building this motor is in could cause a major problem for the company. There is a generator on the switchgear but that only would come on if power is lost to all the switchgear.
    What is the best way to protect critical equipment when only parcal power is lost? There are about 12 main switchgear breakers.
    It could be atleast 1 hour before someone can get to this 3/4 hp motor to make a fix should it lose power. Would a ups work ?
    If you go with a UPS, make sure that you use PF correction caps on the motor because most if not all UPSs are only capable of a small amount of reactive power. For example, I have an APC smartUPS 3000 at home on my computers. Its load ratings are 2200 watts or 3000 VA.

    If you go the UPS route, I would go with at least a 5kVA unit. You need something capable of the inrush currents and the bad power factor while having sufficient battery power to keep it running until the generator can start.

    Just for a data point, I ran an old 1/2 HP washing motor on it and found that the this particular unit is barely capable of running the motor on battery but can only start it if the UPS is on AC.

    Here is what I would do:
    Find the power factor of the motor by measuring it. Calculate and install enough capacitance on the motor to get the power factor at a value of 1 or unity. Get a UPS that is at least 5 kVA. Get a generator that will automatically start and a transfer switch. You may have to put the the transfer switch AFTER the UPS because some UPSs will not accept the generators power due to frequency and voltage fluctuations. Wiring it this way is different from how its done on larger systems but may be needed in this special case.

    The idea is that the UPS would hold the motor while the generator starts and gets up to speed. Once its online, the transfer switch would switch from the UPS to the generator. The UPS would then either idle on battery power or shut down until AC is restored. Once this happens, the UPS switches to AC, the transfer switch moves the load to the UPS and the generator shuts down.

    Sorry for writing a book. If you have any questions, let me know.