bond service entrance raceway gutter

Status
Not open for further replies.

FWD

Member
Two questions , is it correct to bond the service entrance grounded conductor in the service entrance raceway or gutter ? , as one of several options listed , grounding lock nuts , bushings and bonding jumpers ? Is it legal to connect the grounding electrode conductor to the grounded conductor in the service entrance raceway ?
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Connecting the neutral to the service raceway in an approved manner is one way to accomplish the requirements of 250.92.
The grounding electrode conductor can be connected to the neutral in the wireway also. This is helpful when you have mutiple service disconnects.
 