Nelson Abram

Nelson Abram

Ok, so there is no where in the code book that says that you that you are required to have a exterior receptacle (i.e plugin) on the exterior of a garage. I don't access to a code book but I wanted to get some facts about this issue before I take it up with a higher authority. Any information would be greatly appreciated.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The NEC does not require an outside receptacle at a detached garage, it dose require one inside, that is in 210.52(G) If your area has local codes it may be above what the NEC requires.

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The nec only requires an outlet in a detached garage if you have power run to it-- surely you will, but there is no requirement to have power out there.

Take note of this section

210.52(G) Basements, Garages, and Accessory Buildings. For one and
two- family dwellings, at least one receptacle outlet shall be
installed in the areas specified in 210.52(G)(1) through (3).
These receptacles shall be in addition to receptacles required
for specific equipment.
(1) Garages. In each attached garage and in each detached
garage with electric power, at least one receptacle outlet shall
be installed in each vehicle bay and not more than 1.7 m
(51∕2 ft) above the floor.
(2) Accessory Buildings. In each accessory building with electric
power.
(3) Basements. In each separate unfinished portion of a basement.
 